Electrical breaker pops question

Posts

Electrical breaker pops question

#1

Electrical breaker pops question

jeff

>Hi all

I plugged my jointer in to test and the breaker popped.

The motor started and was ramping up to full speed when the breaker finally popped.

This is a 3hp 220v motor. 20 amp circuit breaker on #12 wire.

I normally use Square D breakers that have a pretty good overload rating.

So, switched to another outlet and it fine.

Anyone know how much the motor will pull on start-up?

I'm trying to figure out if I just have a bum breaker or I'm too close to the overload rating.

I can rewire and upgrade to 30 amp, but it's a pain in the neck in this spot (The wall is closed up).

I don't have a peak ammeter to test the start-up current draw.

Oh, I do all my own electric work normally.

jeff

Re: Electrical breaker pops question

#2

Re: Electrical breaker pops question

Tom MacGregor

>You could switch the hot wire with another 20A breaker already in the panel to see if it still pops. You wouldn't need to remove either breaker or do anything to the two neutrals and grounds. Just shut off both breakers before you switch the hots. If it worked OK in another outlet you probably have a breaker going bad.

Re: Electrical breaker pops question

#3

Re: Electrical breaker pops question

jeff

>Tom

Good idea.

I'll just pop in a spare breaker.

I still would like to know how close the breaker is to the draw.

Jeff

Re: Electrical breaker pops question

#4

Re: Electrical breaker pops question *LINK*

Larry Marker

>Does the motor have a nameplate on it? It should and it should have the starting current requirements on it. Look for a value called LRA (Locked Rotor Amps) -- you should see a code letter.

See the link below for an explanation.


NEMA Code Letters

Re: Electrical breaker pops question

#5

Re: Electrical breaker pops question

Will Abbott

>most likely you have a bad breaker. almost all breakers have a time delay before they will trip, to allow a motor to start. the other possibility is that you are getting voltage drop because of the distance from the panel to the machine. you normally only see this if you are more than 100' from the panel. so if the machine starts fine on another circuit and you are not real far from the panel, i would replace the breaker.

will.