Circuit/breaker size for new compressor?

Posts

Circuit/breaker size for new compressor?

#1

Circuit/breaker size for new compressor?

Tony Sade (Charleston, WV)

>I'm buying a new compressor to run nail guns, staplers and and an HVLP conversion gun, and for filling up tires and such, and am wondering whether the circuit I have is sufficient. Wire is #12 copper connected to a 20A breaker. The line technically isn't "dedicated" to the compressor, but the only thing connected is a 4-outlet box. Nothing else will be running while the compressor is in use.

The compressor, a 3.5 hp, 20 gal. Quincy, is 115 volts, and will peak at 15 amps, I'm told.

Am I good?

Thanks,

Tony

Re: Circuit/breaker size for new compressor?

#2

Re: Circuit/breaker size for new compressor?

Bill Howatt

>If the plate says 115V, 15A then it is likely made to run on a regular 15A circuit. The 3.5HP is a number that has little basis in normal operation - the maximum actual running HP from a 15A circuit is about 1.5HP. My 5HP compressor runs on a 115V, 15A line with no problems and it is spec'd at 15A. Compressors have an unloader so they don't start under load.

Bill

Re: Circuit/breaker size for new compressor?

#3

Re: Circuit/breaker size for new compressor?

Larry Clinton At Frankfort (Central)., Indiana

>You really don't size a breaker to the machine. The breaker is installed and rated to protect the fixed structure wire and associated receptacle ONLY. This is true with all machinery and wiring. If the breaker is large enough to start the compressor and the current stays near that level, the motor will burn up. The breaker does not protect your equipment. The motor on the compressor will have it's own protection, usually a thermal breaker. So as long as the breaker and wiring is rated to carry sufficient current, it is the "right size". If you think the breaker may be too low in current carrying capacity, install a larger one (say a 30 amp) with the proper (10 gage) wire. It will be the "right size" (as will any larger circuit).