>I need to run a 220 line for a couple of tools. The line will be hung high on a basement wall, out of the way, but still exposed, so I want to protect it. To give myself flexibility down the road, I plan on installing 5 outlets, but likely never using more than 2 at one time.
I don't want to mess with metal conduit, so I am considering using metallic cable. I can buy the metallic cable at HD for less money than buying the #12 single strands and running them in conduit. I have never used the metallic cable before, and I'm not sure of a small detail in connecting the cable to the metal box. The connectors are sold with plastic/nylon plugs. I'm sure these are to prevent scraping of insulation, but I am not sure where/how they are to be used. Do these insert into the metallic cable?
>As already stated, the plastic bushings are for protecting the wire from the edge of the flex.
Regular romex clamps (C-500)will work but there is a special connector made just for flex cable. I think they are called C-550s. The "C" connectors for romex and various cables are desingnated as if the fractions were in decimals. A 1/2 connector is a C-500, a 3/4 is a C-750, etc. up to C-2000 for large SE cable.
Don't let them sell you connectors for greenfield cable. They might work but will probably cost a lot more.
The most fun you will have is cutting BX without cutting the wire. It can be done by cutting diagonally across the rib with a hacksaw, but it's easier (once you get used to it anyway) to do it with diagonal cutters, aka dikes. If you have a lot of it to cut it might pay to buy one of the special cutters made for the purpose. I somehow managed to wind up with two, one by Greenlee and one by Lenox.