teflon_jones

>I recently got a Delta DJ-20 and was working on the wiring tonight but I'm not sure if I'm doing it right. I'm re-using a 220V circuit that has 4 wires, but the plug only needs 3 wires. The instructions on the plug say to connect the hot wires to either side and then the ground to the green screw. I have a black, red, white, and bare ground in my wiring coming from the panel. The instructions are clear and easy on connecting the red and black wires to the screws on each side of the plug, but I'm stuck on the ground. I have both the white neutral wire which is also called a ground, plus the bare wire ground. Which one do I connect to the green ground screw?

I think I connect the bare wire, but I'm not sure. I don't want to fry my brand new jointer! I don't think the white wire gets used in this setup and I think I need to just stick a wire nut on it and cap it. The plug on the jointer looks like a standard grounded plug with two flat pins and one round pin, except the flat pins are rotated 90 degrees. For anybody unfamiliar with this setup, that prevents you from plugging it into a 110 outlet. In most 3 wire 220V setups that I'm familiar with, there's no bare ground wire and there's three flat pins and no round pin, so it's easy to wire it.

Thanks in advance for any help!!!

Re: Need help with my jointer!

#2

Re: Need help with my jointer!

Larry Clinton At Frankfort (Central)., Indiana

>You are correct. The Red and Black are the "hot" lines with 240V between them. The ground wire is bare. The white wire is a "Neutral". This is at the same potential as the ground - it is used when a device has both 120V and 240V requirements. Either "hot" wire has a potential of 120V to the white "neutral". In your case since the equipment does not need 120V, you can wire nut or tape off the neutral. An example of a reason for the neutral is when you have an electric clothes dryer which uses 240V for the heaters and 120v for the timer and/or light bulb. Older wiring codes did allow the bulb to have the current return on the ground - this is no longer allowed in any wiring.

Re: Need help with my jointer!

#3

Re: Need help with my jointer!

teflon_jones

>Thanks Larry, I appreciate the response! I thought I had it right but with a $1000+ piece of equipment I'd like to make sure. :-)