>If a plug for 110 volt machine fit into a 220 volt outlet then I would say it is not wired according to code and is in fact a life threatening situation that I would put at the top of my list to correct. But then I am not an electrician and don't know much about it.
>I agree with Moses. You need to double check your plugs and receptacles and be sure they are correct to avoid hurting yourself. Not that mine are the standard others should go by, but none of my 220 outlets permit the insertion of 120 plugs.
>No, that shouldn't be it. An induction motor spins at a speed determined by the frequency of the power applied, not the voltage (at least as soon as there is enough applied to overcome losses and friction).
>Many years ago I was working for an electrical contractor who sent me to one of the local lumber yards to fix an indusrial sized radial arm saw. (Boy, do I wish I knew what happened to that saw.) It was big enough that the start capacitors were in a box seperate from the motor and all that was needed was to solder a lead back to one of the capacitors.
I was kinda green back then and it never occured to me that a saw that big would run on something other than 110. Needing a place to plug in the soldering gun, I unplugged the saw and plugged the gun into the outlet the saw had been plugged into.
If you think your drillpress on 220 was impressive, you should try a Weller soldering gun. Not, understand, that I would recomend actually trying it.
Lesson learned: When in a workshop, don't assume the voltage in a receptacle based on the receptacle itself. Particulary in a lumber yard/ hardware store setting it can easily be a case of "Joe" using what was handy instead of what was correct.
>Its A 220 RECEPTACLE. Roundhole bottom, normal prong hole upper right, "cross" shaped pronghole upper left. 220 plugs on my 220 machines fit in fine, so does the 120 from my drill press tho !
>I would say that someone didn't put the proper outlet in. It sounds like a 20A, 110V outlet to me. 220 outlets are usually upwards of $10, while a 20A 100V will only be a couple bucks.
I would put a proper 220v 20A outlet on it. You will also need to change the plug on your drillpress to match it. This will not happen again.
As far as the motor, you can rewire most 110 motors for 220. What I would think happened is that the wiring coils kept trying to pull the motor armature back and forth with the alternating current. I have seen this and it usually will not permanently damage the motor as long as you shut it off soon.
So there is no misunderstanding, the attached image shows the NEMA receptacles that are sometimes confused. The receptacle images are stolen from the web site in the link below.
As Brian mentioned, based on your description it seems that someone who didn't understand may have installed the wrong outlet (and plug) for your 220v device. If your comment that "plugs on my 220 machines fit in fine" means you have more than one such outlet, the problem is worse.
If the wrong receptacles and plugs have been installed, this should be corrected ASAP to prevent permanent damage to 120v equipment someone may accidentally plug into one of these outlets. Even better, it may prevent a family member or future owner from dying a painful death by electrocution or fire.
Until it is repaired, perhaps you could spray paint the outlet(s) bright red and tape a cover on top labeled "CAUTION: 240 VOLTS - NOT A 120V OUTLET".
>dUDE YOU GOT IT EXACTLY RIGHT. Dang keep forgetting to turn off the caps lock (we have an app that chooses it for you when its launched)
One of the receptacles on that circuit is , in fact, the non 220 20 amp type you showed.
re: "If the wrong receptacles and plugs have been installed, this should be corrected ASAP to prevent permanent damage to 120v equipment someone may accidentally plug into one of these outlets.".....