>Because of a repeated failure of the pressure relief valve on my hot water heater and a toilet "whistling", I decided to test the water pressure in my house. A reading of 128 psi indicated it was time to replace my pressure reducing valve.

A quick trip to "big orange" revealed only 1 PRV. It's made by Watts model N55BU M1. Is this valve ok or am I going to be replacing it in a couple of years because it's a 'cheapie"?

Thanks for any input.

Re: OT Plumbing Question

#2

Re: OT Plumbing Question

Binen

>You should not need to replace the entire pressure valve. If you have a good quality valve now you should only need to replace the diaphragm in the valve. Replacing the diaphragm should only take a half hour at most and not cost very much. If the valve you have has a diaphragm that is not replaceable then look for a good quality valve where it can be replaced as needed. The diaphragm should last years.