OT: Hot tub suddenly tripping breaker

Posts

OT: Hot tub suddenly tripping breaker

#1

OT: Hot tub suddenly tripping breaker

Mike Schwing from Md.

>Hi all. Looking to get some thoughts on this before calling in for service. We have a hot tub on the back deck that has been operating properly for more than a year. Yesterday the breaker tripped while I was in the tub with just the number 1 pump running on full. After a breaker reset it appeared to return to normal. The same thing happened to Mrs. Schwing last evening.

The tub is on a 60amp breaker with a "test" feature. The test button correctly shuts the breaker.

Nothing else has changed other than I filled it up a little bit higher than normal, in anticipation of the end of the water supply from the hose due to upcoming freezing temps. The breaker does not trip during the maintenance cycles when the pumps run on low.

Any thoughts? I'm no electrical whiz but a short does not seem likely to me. Perhaps a motor going bad? Anything that I can do to triage the situation?

Thanks.

Re: OT: Hot tub suddenly tripping breaker

#2

Too much Thanksgiving Stuffing?

Barry Irby

>

Re: OT: Hot tub suddenly tripping breaker

#3

Re: OT: Hot tub suddenly tripping breaker

Mark Mandell - Gone Round In Jersey

>Mike,

Call in the pro. What you're describiing sounds like a groundfault interruption that may be caused by a wiring insulation issue having developed from pump vibration over the past year.

Um, BTW, don't use the tub 'till fixed. Nobody wants Fried Schwingding for Christmas.

mm

Re: OT: Hot tub suddenly tripping breaker

#4

Re: OT: Hot tub suddenly tripping breaker

Mike Schwing from Md.

>Thanks Mark. I've got them on the phone now.

Re: OT: Hot tub suddenly tripping breaker

#5

Re: OT: Hot tub suddenly tripping breaker

JoeW in Detroit, MI

>I just tried to work on one for a friend a few weeks ago. This particular unit had two motors. It had the same problem. The unit was equipped with a timer. One cycle of the timer was OK, but the second time you hit the timer the breaker would sometimes trip. It turnd out to be a bad motor. The bearings had gone bad.

If you have a clamp-on amp probe, open your subpanel and amp probe the lines. If you see a rise in the current draw, it is probably the motor going bad. A ground fault will not cause a rise in current.

Joe

Re: OT: Hot tub suddenly tripping breaker

#6

Re: OT: Hot tub suddenly tripping breaker

Marc Evans

>Hello,

I have had a Sundance spa for a number of years. It had an ozone unit that was the buld type. I typically saw the breaker trip rather unpredictably when the ozone unit was going bad (typically 1 - 2 years). Unplugging the ozone proved to reliably correct the problem and replacement was easy.

There are other cheaper things that I have had to replace (like flow sensor and temperature sensor) - these shut the spa down w/o tripping the breaker in my case.

Other than that, motor or circ. pump if you have one...

Marc

Re: OT: Hot tub suddenly tripping breaker

#7

thanks guys, here's what I think it is

Mike Schwing from Maryland

>I took the sides off and started pump 1, in circulation mode, no problem. In high speed mode, water blows past the seal, all over the motor, eventually soaking the windings enough to short the circuit, tripping the breaker.

I took the motor out today but can't get the pump head off, so I'm off to the service center on Monday. Of course, I broke a PVC plumbing elbow while I was in there in the most awkward of spots. So another repair follows this one. Da**it.

Thanks for the advice.