Ron in Drums PA

>Ok, I'm not as smart as I thought I was. Or maybe I need my coffee to kick in!

I have the 220v line fished to where I plan on branching off to two 110v lines. I used 60' of 12/3 and didn't tie it into the breaker box yet.

On 110v lines I'm used to three wires, Hot, Return and Ground. Now with the 220v line I have Hot, Hot and Ground. Each branch will have a Hot and a Ground. So what do I use as a return?

TIA

Re: Another Wiring Question

#2

Re: Another Wiring Question *LINK*

Rod Rentz

>Ron, with the 12/3 wire, your circuit breaker should be no larger than 20 amps. For safety's sake, install a subpanel at it's termination and run your 110 lines from there. This gives you the ability to add additional circuits later (including 220). The following link explains a subpanel pretty well:


http://www.hammerzone.com/archives/elect/panel/sub_panel/01/new.htm

Re: Another Wiring Question

#3

Re: Another Wiring Question

Rod Peterson -*- Ormond Beach, FL

>If you truly used 12/3, there are four wires in it—one black, one red, one white, and one bare. The white one is the neutral or return. The bare one is the ground.

If you only have a black, a white, and bare, then you have 12/2, which is the wrong cable for your intended application.

In non-metallic cable (Romex), the ground wire isn't counted in the nomenclature of the cable—i.e. xx/2 has three wires, xx/3 has four wires. Cord (such as SJ), on the other hand, does count the ground (which is also insulated and green), and is also the wrong cable for your intended application.

Rod

Re: Another Wiring Question

#4

Re: Another Wiring Question

Dan Donaldson

>I you have 12/3, you should have a red, a black, a white, and a bare. If you used regular 12/2 that has a black, a white, and a bare, it won't work for your application. With 12/3, the red goes to one circuit, the black to the other, they share the white, and the ground (bare) goes to everything.

Re: Another Wiring Question

#5

Re: Another Wiring Question

Ron in Drums PA

>I told you my coffee didn't kick in.

Yes it is 12/3 and it has four wires.

Boy do I feel dumb

Thanks Rod

Re: Another Wiring Question

#6

Re: Another Wiring Question

Ron in Drums PA

>Thanks Rod, I think I will do that

Re: Another Wiring Question

#7

Re: Another Wiring Question

Ron in Drums PA

>Thanks Dan

Re: Another Wiring Question

#8

This is not necessary

Rick Christopherson

>There is absolutely no safety concern, code requirement, or anything else for this circuit to warrant the need for a subpanel.

The original poster was describing a multiwire branch circuit, which is fully covered by the NEC. All that is required is a simple junction box at the point where the two circuits diverge.

One requirement for multiwire branch circuits it that you cannot use any device (i.e. receptacle) to connect wires together. You must use pigtails to connect the outlet to the circuit. In other words, you cannot connect incoming power to one side of an outlet and connect outgoing power to the other side of the outlet.

Contrary to previous NEC requirements, you no longer have to use a 2-pole breaker (reference NEC 210.4) unless the multiwire branch circuit supplies both 120 and 240 volt loads, or unless both hot wires are connected to the same yoke (i.e. one outlet with both circuits present).

Re: Another Wiring Question

#9

Question

Ron in Drums PA

>Are you saying that I can't have two outlets (each in a different box) on a branch?

Re: Another Wiring Question

#10

No

Dan Donaldson

>What he is saying is that the rules are different if you have one outlet and wire the top half on one circuit and the bottom on the other. You can distribute the other plugs just like normal, except as was mentioned, you have to use pigtails on the outlets and not wire through them.

Re: Another Wiring Question

#11

No

Rick Christopherson

>You are permitted to have outlets on separate circuits, and yes, you can even have them inside the same junction box too. As Don also stated, I was referring to having two circuits on the same duplex outlet, where the top plug is one circuit and the bottom plug is another circuit.

Just to make sure you understand, what most people call "an outlet" is really called a "duplex outlet" because there are two plugs (top/bottom). Normally these two outlets are connected together by a little tab on the side of the outlet, but if you break off this tab, then you can wire each one separately, if needed.

This is the point I was stating previously. If you wire two circuits to the same duplex outlet, with the tab removed, then you must use a 2-pole breaker so both circuits turn off simultaneously. Since you were probably not planning on doing this, then you do not need to worry about this information.

Re: Another Wiring Question

#12

Thanks

Ron in Drums PA

>Thanks for clearing that up guys, I would have sure hated removing those outlets