>Yes, your assumptions were correct. No, you do not need a 2-pole breaker for this setup. There is nothing stopping you from using the 2-pole breaker if you want, but there is nothing requiring it either.
At 70 feet, you are below the length for derating the circuit, so you can still use #12 wire for a 20-amp circuit. If these are general purpose outlets, then this is fine. If these are high-demand outlets where you would expect to be drawing nearly 20-amps on a routine basis, then you may wish to step up to 10/3 for your feeder wire, but you could still use 12/2 for the two separate branches.
Because these two circuits will be sharing the same neutral (using 12/3 or 10/3 romex) then you do need to make sure that your breakers span both phases of the load center (i.e. check the voltage to make sure you have 240 volts between the two circuits). Simply using a 2-pole breaker does not automatically guarantee this either on all panels. If you do not span both phases, then the current through the neutral wire will be additive and you will exceed the capacity of the wire.