Re: More info for anyone interested...
Rick Christopherson
>John,
Unfortunately, using a multimeter to diagnose a ground problem may not always give you reliable results without a few extra checks. The continuity test you did on the ground prong to the metal chassis is probably the most reliable indication that the saw is not your problem. My original thoughts back when this discussion started were leaning toward a house wiring problem, but when you said the house was so new, I didn�t want to go down that road needlessly.
See if you can check the voltage from the saw�s top to various other tool grounds in the shop. I am guessing that you will show nearly zero volts to any other tool chassis. If that is correct, then the individual circuit grounds are also not the problem.
What remains is how well your house�s grounding system is connected to the Earth itself. There are a couple of possibilities.
- You have a poor grounding connection at the ground rod.
- You have a poor grounding connection at both sides of your water meter.
- You have poor soil, and the grounding electrodes (ground rod plus water pipe) are insufficient for the soil conditions.
- You have an excessively large leakage current in your grounding system, which is elevating the ground voltage of the soil near your ground rod.
The first two are relatively easy to check. This is also a case where you want a digital volt meter if possible. Check all of the voltages between both sides of your water meter, the ground rod itself, and the chassis of the main load center. All of these should have a voltage less than 1 volt on a digital meter.
Items 3 and 4 are a little harder to check. For item 4, you would need a clamp-on ammeter that you can place around the ground wire that is leaving your load center and going to the ground rod and water meter. You should have some current flow through the ground wire, but not an excessive current. I checked mine a couple of years ago and I was surprised to see that it was somewhere between 10 and 15 amps. I would actually consider this to be toward the high end depending on the total load of the house.
Checking item 3 requires a good Earth ground that is isolated from your home�s grounding system. For simply testing this theory, maybe even a long screwdriver driven into damp soil would be sufficient.
If you are getting affirmative results for either 3 or 4, then you may want to consider adding one or more additional ground rods to your system, especially near your shop. Each new ground rod needs to be connected back to the main ground rod with a #6 copper wire. In some parts of the country, it is not uncommon for multiple ground rods to be required as the norm, due to poor conductivity of the soil.