My house is served by 2 units, one for each floor. One of the exterior units frosts up on the outside, even when the temps are above frost temps but still cool enough to need heat.
Why is this? Why just one of them? Is it indicative of a problem, if so, what is the remedy?
>Mike, in AC mode this may indicate the freon is low. In heat mode, these things usually go through a defrost cycle and maybe yours didn't yet. I'm not sure but it might indicate low freon as well. I'd get it checked out either way.
We just replaced our upstairs unit this summer (on the hottest day of the year). The original was almost 11 years old and had a number of leaks in the cooling coil in the air handler unit. The lines were frosting up along with the outdoor coils because of this. I've had that unit serviced for low freon in past years but the leaks got to be too big. Our downstairs unit hasn't given us a moments trouble so far. I replaced the unit with a new 3-ton Trane and haven't looked back.
>Mike, You mentioned that it was cold enough to extend heat but not cold enough for there to be frost outside. So, It's a heat pump, not an Air Conditioner and its a cool fall day, but not below freezing out doors.
That's what heat pumps do. They are air conditioners that run backwards and forwards. In the heating cycle, the outside unit gets cold, absorbs heat out of the atmosphere and then pumps the heat into the house and blows it out. As that outdoor coil gets cold, condensation forms on the fins and tubing. As it gets colder, it frosts up. The weather affects this. when it is humid there is more condensation/frost. When the RH is very low, there is less. It is also related to the demand from the house. The longer the unit runs the more time there is for frost to form.
David is right, there is a defrost cycle. Some units do it based on time, they just defrost every so many minutes regardless. Higher efficiency units have a frost sensor and only defrost when necessary. (The Defrost cycle is very "expensive". The unit reverses and runs and an Air Conditioner, taking heat from your house that you have already paid for and pumps it back out to the outdoor coil, melting the frost. So you won't notice the AC coming out of your ducts, the unit turns on the electric back up or strip heaters and produces electric resistance heat to offset the Chill and reheat the air. At triple the cost of the heat produced by the Heat Pump.)
So why one unit and not the other? Usually the first floor unit runs more than the second floor unit. Warm air rises from the first floor the the second floor so often the lower level system does most of the work in the winter and the second floor unit does most of it in the summer. So It could be that the unit that is frosting up is running more. You might have that unit set warmer than the other one, causing it to run more.
Are the outdoor units side by side? One could be located in the shade or behind a bush or in some sort of micro climate that encourages it to frost up? (Dryer vent blowing on it? ETC.
And it could be that one or both units needs servicing and tuning. It's possible that the other unit needs refrigerant and that the outdoor coil is not getting as cold as it should. Maybe it should be frosting up too if it were running well.
You can check them yourself. Its hard to do without bringing the strip heaters on. Turn them up one or two degrees so that they run but do not have the Emergency) Heat on. With a thermometer, take the temp at the air return. After the system has run for a few minutes, take the temp at a supply (close to the air handler if you can). You are looking for 14 to 20 degrees difference between the two. The "trick" is to get the system to run for more than a few minutes without cranking it up so far the strips come on. You may have to cycle it more than once. If the Temp, Difference is less that 14, you Probably have low refrigerant. If it is more than 20 you probably have restricted air flow. ("Probably", because there are many other possibilities.)
A service technician can do a much more sophisticated diagnosis.
Thsi is also a good time to look at the inlet side fo the indoor coil and see if it is clean. (It should be)
I assume the unit that is frosting up is connected to a separate air handler from the OK unit? Have you changed the air filter in the last 10 years or so 8-). Seems like I remember that a very clogged filter can cause the same problem, in addition to low Freon. Let us know what the HVAC service folk find out.
The unit that was frosting up was very low on Puron. No leak was detected but they will come back out and check it in a month. They suggested that it was probably installed that way originally 5 years ago. Coils were clean, everything else was in good shape.