>I fnially took my new/old 1966 Powermatic 12" planer apart this weekend. I was able to take the motor out to be able to see the plate. It is a Century 4hp, the amp rating is 15amps.

So with that info what do I need for a breaker and wire?

Thanks!

Re: Motor Question-Again.

#2

Re: Motor Question-Again.

Jim Swank

>I would run at least #12 wire and a 20 amp breaker. I'd consider running #10 wire if it's very far from your panel, or even just in case.

I'm sure someone will point out that #14 wire and a 15 amp breaker will handle the rating on the nameplate. That would be true, but it leaves no reserve and saves very little, even at today's copper prices.

Re: Motor Question-Again.

#3

Re: What voltage, Tom?

Al Stokka - Cambridge, Iowa

>

Re: Motor Question-Again.

#4

Re: What voltage, Tom?

Tom Norton

>230v

Re: Motor Question-Again.

#5

Re: Motor Question-Again.

ehgauss

>If your motor is a true 4 HP, that converts to about 3000 watts (746 w/HP) at full load. But motor efficiencies are usually only around 90% (for really good motors), so the power draw from your electrical system will be about 3333 watts (3000 divided by 0.9), again, at full load. However, since the current to an inductive load like a motor always lags the voltage, you have to apply a "power factor" correction. For most motors, I recall that 80% is a reasonable assumption. Dividing 0.8 into the 3333 watts gives about 4170 volt-amps. Dividing 4170 by 230 volts gives a current of about 18 amperes. Therefore, you could go with a 20 amp breaker and AWG#12 wire, and still be able to run at full load. However, it would be a much better practice to give yourself a bit more margin. I'd go with a 30 amp breaker and #10 wire. On the other hand, if your planer will rarely operate at or near full load, you could get away with 20 amps and #12. Hope this helps. Gene Gauss

Re: Motor Question-Again.

#6

Re: Motor Question-Again.

Larry Clinton

>Personally I would install a 30 amp breaker and 10 gage wire. If your current planer wears out or if you just get an "itch" to replace it with a larger one, you may find the 20 amp circuit inadequate. I currently have a 20" planer with a 5 hp motor & it requires a 30 amp circuit due to starting inrush current. Remember the breaker is only sized to protect the permanent (structure) wiring. The motor is protected (normally) with an internal thermal protection device. The additional wire size and breaker probably won't increase the cost of installation very much, and insures you future compatibility with larger tools.