Re: Motor Question-Again.
ehgauss
>If your motor is a true 4 HP, that converts to about 3000 watts (746 w/HP) at full load. But motor efficiencies are usually only around 90% (for really good motors), so the power draw from your electrical system will be about 3333 watts (3000 divided by 0.9), again, at full load. However, since the current to an inductive load like a motor always lags the voltage, you have to apply a "power factor" correction. For most motors, I recall that 80% is a reasonable assumption. Dividing 0.8 into the 3333 watts gives about 4170 volt-amps. Dividing 4170 by 230 volts gives a current of about 18 amperes. Therefore, you could go with a 20 amp breaker and AWG#12 wire, and still be able to run at full load. However, it would be a much better practice to give yourself a bit more margin. I'd go with a 30 amp breaker and #10 wire. On the other hand, if your planer will rarely operate at or near full load, you could get away with 20 amps and #12. Hope this helps. Gene Gauss