Partially correct.
Rod Peterson -- Ormond Beach
>> There is a condition where you can wire two 120 volt circuits from a double circuit breaker normally used for 220 Volts.
Yes. This is a “multi-wire branch circuit.”
> Lets say you wanted two 20 amp circuits in your shop or kitchen of where ever.
Probably a more common application (and the one which was used in two separate instances in my house—wired in 1973) is two bedrooms or a bedroom and a bath (back when there wasn't a 20A requirement for the bath). I don't like them, though, because, as you said, they can be confusing to homeowners.
> You can save a few pennies by using a double breaker and running a 12/4 with ground to the first outlet box.
I hope that was a typo. To my knowledge there is no such thing as 12/4. In any event, 12/3 is all that's needed. Although back when I worked in a hardware store it was possible to buy non-metallic cable without a ground, I'd be surprised if you could find it anywhere today, thus the with ground is implied when talking about NMC, and it isn't included in the wire count (jacketed cord is a different story, but we're talking about house wiring, and cord isn't).
> You use the black, white and green in the normal fashion, In the nest bow you use the Red White and Green.
I hope that's a typo, too—I'm guessing next box. I'm not trying to ping on your spelling or typing, but as you well know, these electrical threads are tricky and there are a lot of ignorant (lacking knowledge—not stupid) folks reading these posts for information.
It looks like you're describing a system in which the xx/3 is run through several sequential boxes, with every other box being fed by a different circuit (of the two). I definitely don't care for that technique. Even though code doesn't preclude it (and doesn't require the two pole breaker unless both circuits are connected to a common yoke—such as the two halves of a duplex receptacle with the jumper broken off), I have never liked the idea of there being two circuits worth of electricity in one box (excepting the load center or an obvious 240V circuit).
(Barry, ignore the following—it's for people who might not be aware of the concept behind the multi-wire branch circuit)
What makes the multi-wire branch circuit work is the fact that the two hots (taken from opposite poles of the load center, and the principal reason why a two pole breaker is a good idea) share the neutral. Since the hots are 180° out of phase, the currents in each are additive, but opposite in sign (because of the phase relationship). That essentially means that whatever current appears on one wire is subtracted from the current on the other to determine (the absolute value of) the total current in the neutral. Consequently, the maximum current that can appear on the neutral is whatever the highest value is in any one leg.
Rod