Re: 220v circuit question
Mark Mandell - Gone Round In Jersey
>Tom,
Code allows a maximum breaker of 25 amps on a #12 circuit. However, when I run a 220 line, I invariably use #10 for the option of a higher ampacity limit/use even if I undersize the breaker for safety. Gives me the option of increasing the breaker later if needed. Case-in-point was my air compressor located in the garage. I-G (real) 3hp unit that I breakered for 20 amps. During the Summer it was fine, but when the cold weather set in in my unheated garage, the start phase would blow the lite breaker getting that cold pump to spin up. I put in a 30amp breaker and all's well all the time.
You planer may be just fine and dandy on 20 amps doing 6" stock until you run a wide board through that's gonna pull some serious juice. If you're going to real 4 or 5 hp, I'd opt for the heavier wire (10/2 wg) in copper and a 25 or 30 amp breaker.
mm