Two 220V machines on one circuit?

Posts

Two 220V machines on one circuit?

#1

Two 220V machines on one circuit?

wilbur

>I have a 1.5 HP dust collector that I posted about last week. The motor is rated to draw 16 amps at 120V, and 8 amps at 220 V. It trips the 120V 20A circuit that it sits on pretty regularly on startup. After doing some troubleshooting, I'm considering converting the motor to run on 220V instead.

The main problem is that when I wired my shop, I made provisions for a single 220V 20A circuit and outlet. A jointer planer combo machine with a 2 HP, 220V / 8.9 amp motor is plugged into this circuit.

I think I'll just install a second 220V circuit for the dust collector, but I was wondering if anyone would run two 220V machines on a single circuit. If I connect a second 220V outlet to this circuit, with a total constant current draw of 17 amps between the two machines, I think that this would be too close to the 20A capacity of this circuit for comfort.

Am I right on this point? Does anyone have two 220V machines on a single circuit?

Re: Two 220V machines on one circuit?

#2

JL

Re: Two 220V machines on one circuit?

JL

>I have two 220 V machines on one circuit. But they are not machines that I would be using at the same time. Go ahead and run a separate circuit like you were thinking.

Re: Two 220V machines on one circuit?

#3

Re: Two 220V machines on one circuit?

Bill Howatt

>I have a TS, jointer, stationary sander, 2 shop-built air-cleaner fans on one 240V circuit. I have a lathe and vacuum pump motor on another 240V circuit.

There is nothing magic about 240V circuits other than they don't have a neutral. You can have more than one receptacle on the circuit but you can only run as much stuff simultaneously that the breaker will support.

As far as your DC and your jointer/planer goes, you can probably get away with it by starting the one machine and then a couple seconds later start the other machine so you don't have a combined starting current surge. The DC may run close to its rated current but the jointer/planer only will when fully loaded. For light cuts you may be drawing less than half current. Also, breakers when they hit their rated limit do not necessarily trip immediately (it depends on the particular breaker's age, how accurate its components are). You may be able to run with a 10% or more overload for a few minutes.

Try it and see how it works then decide if you want to add another circuit or just bite the bullet and do it.

Bill