Re: OT- wiring subpanel in outbuilding
Rick Christopherson
>Given that this is just a garage where you need lights and a couple of outlets, you can keep your costs down and keep this simple. Contrary to the information in another posting, your #6 wire will support 60 amps, not 30 amps, so you need a 60 amp breaker in your main load center. You might have a hard time finding a single-pole breaker of this size, so you could use a 2-pole breaker with no load on the second pole. (There may be other options, but I want to keep this simple.)
You said you were only carrying two conductors out to the outbuilding, so this assumes that there are no other electrical paths to the outbuilding, and you can have an isolated grounding system. If you have anything metallic running between the two buildings, then you must carry the same ground wire from the house to the subpanel. Regardless, you need a ground rod at the outbuilding. If this is an isolated system with no ground path back to the main load center, then the ground and neutral in the outbuilding need to be bonded. If there is a ground path back to the main load center, then the ground and neutral need to remain isolated at the outbuilding.
Here is a thought for you. If your cost estimates included running a ground wire, yet the buildings are otherwise isolated, then for the same cost, you could run both hot wires without a ground. Even if you didn�t need the 240 volts, this would allow you to down-size the wire while maintaining the same system capacity. It would be a lot cheaper running #10 wire than #6 wire.
Finally, to answer the question you originally posed, yes, you could jumper the hot lugs in the subpanel, but frankly, there is no point. If you only need a couple of circuits, then it doesn�t matter that you skip every other breaker location.
Now to really be devil�s advocate, if all you need is a couple of outlets and lights, then you could get by with a single 20-amp circuit and #12 wire (I would recommend using #10 because this is right on the threshold of 100 feet).
Given all of the above information, my initial impression of this situation is that you haven�t fully thought this out, and you could be doing this better. You are setting this up as though you need more power, yet you are crippling the system. On the other hand, if you don�t need a lot of power, then there are several issues which are costing you more money.