220 VAC cabinet saw plug & recepticle

#1

220 VAC cabinet saw plug & recepticle

David C. Lykins - guitardude - Dallas GA

>Well I finally purchased a new house and have been in a week. Now that it's fairly livbale (not totally unpacked yet) its time to start wiring my basement/shop. I don't have one single receptacle in that shop, and the garage only has one wall outlet. But I have wire, receptacle boxes and recepticals ready to go, with the exception of the 220 VAC (30 Amp) circuit I need for my Grizzly 1023S. I've got a dryer plug on it now as I temporarily plugged it into the dryer receptacle at the house I was renting. Worked great but I'd really like to wire the shop to NEC.

So the question is, which plug and receptacle do I need to get for the saw and the outlet. Home Depot and Lowes have serveral, but I'm just not sure which one I need, and I'm too lazy to read the NEC.

Any help (and pictures) are greatly appreciated.

Thanks!

Re: 220 VAC cabinet saw plug & recepticle

#2

Re: 220 VAC cabinet saw plug & recepticle

Rick Christopherson

>First off, your Grizzly 1023 doesn't need a 30-amp circuit, only a 20-amp circuit. Yeah I know, I've heard the manual says 30-amp, but it is wrong. Your saw is only 17 amps at full load, and it is a non-continuous load, so NEC permits this to be on a 20-amp circuit.

If you already have a 30-amp circuit, then you must use the NEMA 6-30 plug or L6-30 twist lock. You cannot put a smaller plug on the outlet, and you cannot use the dryer plug you currently have.

If it is a 20-amp circuit, then you can use the NEMA 6-20 or L6-20. If your saw was rated for 15 amps (Delta Unisaw) then you could also use the NEMA 6-15.

Re: 220 VAC cabinet saw plug & recepticle

#3

Re: 220 VAC cabinet saw plug & recepticle

Rod Peterson -- Ormond Beach

>Ha, ha—I love how you managed to spell receptacle in every possible way in one post (including the right way).

Okay, on to your question. First and foremost—unless your saw has a 5HP motor, there's no need to go to a 30A circuit. 20A will do just fine for the usual 3HP machine. You can save yourself some money, aggravation, and convenience by sticking with 20A.

Secondly, there are two schools of thought on plug/receptacle combos. Some folks like a locking plug. Nothing wrong with that, especially if you have a ceiling drop (I do, and I have a locking receptacle there—along with a short conversion cord that transitions to a standard NEMA 6-15R for all my 6-15P cordsets).

All of my Delta tools wired for 240V (and my compressor) have a cord with a 6-15P on the end of the cord. Can you guess what receptacles I put into my shop?

The 15A receptacles at both 120V and 240V are okay by the NEC for use on either 15A or 20A circuits (note: they aren't designated 15 or 20 amp for their actual current handling capacity—they're keyed differently to prevent a 20A plug from being attached to a 15A circuit). It's a specific exception in the NEC.

Rod
Addy Protocol: Experienced amateur electrician

Re: 220 VAC cabinet saw plug & recepticle

#4

Re: 220 VAC cabinet saw plug & recepticle

Rick Christopherson

>Well, we made simultaneous postings, but at least we said the same thing.

In reality, I wouldn't hesitate to use a NEMA 6-15 plug on this saw for the reason you stated. However, I am not sure (stress not sure) that this is permitted when the saw it technically rated at 17 amps (if memory serves me). As indirectly noted by both of us, the 3hp Delta Unisaw ships with a 6-15 plug on it, and even though this is rated at 15 amps, it would not be a big deal either way. It depends on how strict to code the person wants to stay.

Re: 220 VAC cabinet saw plug & recepticle

#5

Plugs

Mark Goodall - ATL - tooljunkie

>I fidn this diagram helpful, if only to make sure that the outlets and plugs that are in the bins at HD are the correct ones.

Don't you just hate reaching into a box, pulling out a couple of things (especially plumbing) and discovering that they are not what they are labeled as when you're at the cash.

Happy Woodworking!


img

Re: 220 VAC cabinet saw plug & recepticle

#6

You labeled those, right?

Rod Peterson -- Ormond Beach

>You marked each of the receptacles "receptical?"

Just checking.

Rod

Re: 220 VAC cabinet saw plug & recepticle

#7

Re: You labeled those, right?

Rick Christopherson

>I type that word a heck of a lot more often than most people, and if it wasn't for spell-check, I'd still get it wrong 75% of the time, even though I know it is a word I commonly misspell, and I'm a professional writer. This is a word that I certainly would never fault anyone, especially a non-electrical person, for misspelling.

Re: 220 VAC cabinet saw plug & recepticle

#8

Dang forgot FTP after I'd FTP

Mark Goodall - ATL - tooljunkie

>You know, I remember changing those labels on the diagram a few years ago when you first mentioned it, and I somehow never FTP'ed the new image to the server.

Dang, I must have forgotten to FTP the images after I FTP (Fixed The Picture).

Thanks for reminding me AGAIN ;)

Happy Woodworking!

Re: 220 VAC cabinet saw plug & recepticle

#9

Re: You labeled those, right?

Rod Peterson -- Ormond Beach

>Mark and I are old friends from back in the Badger Pond days, and although the argument certainly could be made that it might have been more appropriate to alert him by the back channel, we frequently exchange good hearted barbs like that in public.

I meant nothing demeaning by it, he knows I didn't, and I know he knows I didn't. I also recognize that if you didn't know of our relationship you could easily have taken it as mean spirited.

Rod

Re: 220 VAC cabinet saw plug & recepticle

#10

Re: You labeled those, right?

Rick Christopherson

>No, I wasn't concerned about Mark, and I did know this was meant in lighthearted jest. It is the original poster who could take this the wrong way, and think that you were making fun of him. You may have forgotten, but you started the jesting with a reply to him before Mark entered the discussion, and he may not have realized that this was an inside joke.

Re: 220 VAC cabinet saw plug & recepticle

#11

Don't forget 630-R and -P. That's what I've got.

Craig Daymon

>

Re: 220 VAC cabinet saw plug & recepticle

#12

Technically Rod, that 15/20 rule is .......

Tim Greif - West of Chicago

>Technically Rod, that 15/20 rule is correct only if you are talking about multiple receptacles on the same branch circuit. If you put a single receptacle (not a duplex, they're considered multiple) on a branch circuit for a saw or tool for instance, it has to be rated no less than the branch circuit. That requirement is on the same page of Article 210 as the one you refererence.

Reason I bring this up is because I think there's a bit of disconnect in the Code as it relates to this. The code at 210.21 B.(1) says specifically "a single receptacle installed on an individual branch circuit shall have an ampere rating not less than that of the branch circuit." There's no reference to the maximum size. Accordingly, I find no place in the code that prevents me from installing a 50 amp receptacle on a 20 amp branch circuit that serves just a single receptacle. Wierd, eh?

Re: 220 VAC cabinet saw plug & recepticle

#13

Thanks, Tim.

Rod Peterson -- Ormond Beach

>I think we don't consider that single receptacle circumstance very often because we don't do it very often—at least I don't. I have single receptacles at all my 240V locations (and yes, they do make 240V duplex receptacles—I used one of them in my radio room in Illinois—you can never have too many amplifiers…), but I can't remember the last time (if ever) I put a single receptacle on a 120V line. Even when I rewired the kitchen in our house remodel, I put in a duplex receptacle behind the refrigerator, yet what else would ever be plugged in there?

Thanks for the heads up.

Rod

Re: 220 VAC cabinet saw plug & recepticle

#14

Who?

Mark Goodall - ATL - tooljunkie

>Who did are you? Rob Ponderson? Roger Ponders? Never heard of you.

Badger, what? What are you talking about?

;) <--- Big smilie grin , for those who might not know.... yes Rod and I go way back to the days when the Badger Pond Woodworking Forum was online. There was someone who always called him, Rob, or something else that was close, but incorrect, so we were always quick to joke about it and call him Rob and other things.

Happy Woodworking!

Re: 220 VAC cabinet saw plug & recepticle

#15

Re: Who?

Rod Peterson -- Ormond Beach

>I just checked my email archives and my earliest email to Mark G. (you know what I mean) is Apr of '99. That marks our earliest email correspondence as ≈ 8½ years ago. We obviously had posted to each other on the forum earlier than that. By my reckoning, by the time the new year rolls around it may be close to ten years that we've known each other. Still never met face to face, however.

I'm also trying to remember how far back David Lykins and I go. I just can't recall if he was on the Pond or not. My feeling is yes, but I don't think we've corresponded back channel, so I can't pin it down. I hope Dave reads this so he can disabuse me of my notion if it's wrong.

Rod

Re: 220 VAC cabinet saw plug & recepticle

#16

Speaking of BP days....

Tim Greif - West of Chicago

>Has anyone ever heard from Bill Hartman? He used to weigh in on almost all the elecrical stuff back then. I don't recall ever seeing another post from him here or anywhere else after the pond closed.

Re: 220 VAC cabinet saw plug & recepticle

#17

Feb '97 ?

Mark Goodall - ATL - tooljunkie

>I moved to Atlanta in Aug.1996, and I think I bought my Unisaw in Feb.1997 and found Badger Pond right around then. I remember that you were one of the first I met there. You were one of the few, that like me, had a website dedicated to woodworking, way back in the early days of web sites.

Happy Woodworking!

Re: 220 VAC cabinet saw plug & recepticle

#18

Wow!

Rod Peterson -- Ormond Beach

>I've been trying to reconstruct the genesis of my website and my very original files (the ones that would help me track the approximate date) must be on an old hard drive which may or may not still be around and which may or may not even be usable. I had worked up a chronology of sorts based on what's on my recently retired computer's drive but the furthest back I could come up with was something around '99. Apparently it was earlier than that. A website up for ten years?!?!! Hard to believe.

What may or may not be hard to believe is the basic look and feel hasn't changed much. It's larger, to be sure, and I have revised (slightly) the episode pages in the Norm's Tools area, as well updating the email and "previous page" links, but most of the changes have been invisible (converting everything to some level of CSS, for example, which I did around 2000). Someone is bound to say it's dated and needs Frames or Flash, but I'm not planning on doing either. I guess I'm just stuck in my ways. I did just validate the main page and the site map page for 4.01 Transitional. See the graphic.

Thanks for the "way-back" Mark. I remember calling you on the phone once around '99 when we had a short layover in ATL around the time our daughter got married. Eight years later and we still haven't split a cup. Damn shame.

Rod's ancient website

Re: 220 VAC cabinet saw plug & recepticle

#19

Re: Speaking of BP days....

Howard Norman

>Bill Hartman, yes that is a name from the BP days. I haven't seen him post anywhere since BP closed.

Howard

Re: 220 VAC cabinet saw plug & recepticle

#20

Re: David Lykins...

Al Stokka - Cambridge, Iowa

>Rod,

David Lykins was in Badger Pond. I kept track of the repondents to the question (on the Pond) about ages of posters and David is on the list.

Al

Re: 220 VAC cabinet saw plug & recepticle

#21

Thanks.________

Rod Peterson -- Ormond Beach

>

Re: 220 VAC cabinet saw plug & recepticle

#22

Rick and Rod - It won't run on 20 amp breakers

David C. Lykins - guitardude - Dallas GA

>Gentlemen, I had this saw set up at a shop where we were making cherry and maple 8-quarter table tops. The "resident electrician" came in and wire the circuit, put a 20 Amp plug on my saw and a 20 amp receptacle. Everytime I turned the saw on the 20 amp breakers would pop. The electrician swore my saw was wired wrong and began to take my switch apart...I almost decked him. Finially I showed him the manual that indicated 30amp start up (i.e. breakes), once he change them to 30 amp the saw ran fine.

I have since run the saw on a 220VAC (30 amp) dryer receptacle and its worked fine. I don't feel confident that two 20 amp breakers will run this saw.

Just my humble experience.

Re: 220 VAC cabinet saw plug & recepticle

#23

Re: I agree with David

Brian in Brighton

>I think you need to use the highest startup load in your calcs, that's how we design machinery. The fuses are designed to handle the highest startup loading, not just the running load.

For my 220 lines I ran 10ga and 30A cb's.

Brian in Brighton