OT - Circuit Breaker question

#1

OT - Circuit Breaker question

Tim Caley - North Little Rock

>What all is involved in upgrading a circuit with a 20 amp breaker to a higher amperage? In the winter time I have no problems running what I need to run from the wall plugs (lathe, dehumidifer, fan, etc). But in the summertime when I throw my window air conditioner into the mix, I keep popping the breaker.

Is it as simple as changing the breaker from a 20 to a 30?

Re: OT - Circuit Breaker question

#2

Re: OT - Circuit Breaker question

Howard Norman-Prescott, AZ

>No, to go to a 30 amp breaker the wire size needs to be increased to #10 wire. Probable a better idea is to put another circuit in for the summer time load. That circuit could be #12 wire with a 20 amp breaker/\.

Howard

Re: OT - Circuit Breaker question

#3

Re: OT - Circuit Breaker question

John Ross

>No...please don't just change the breaker, you could start a fire. The breakers are sized (or should be) to the conductor (wire) that is attached. Remember that the breaker is there to provide safety and prevent the wire from overheating.

There is one simple option: Cut the main power and check that the connections are tight. If you have a loose wire in the main box or at the outlet, this can cause high resistance and cause the breaker to trip. Don't forget to check the grounds. The looseness can be caused by the heating and cooling of the wire during loads. This results in the expansion of the wire and ultimate loosening of the screws. I have been able to get a full turn on some connections.

Chances are that the a/c is a pretty big load though, and you may need to run a seperate circuit.

Good Luck and I hope that helps.

Stay safe,

JohninRI

Re: OT - Circuit Breaker question

#4

JL

Re: OT - Circuit Breaker question

JL

>Run a separate circuit for the AC unit. As Howard said, you can't up size the breaker unless you run 10 gauge wire. Running 10 gauge wire is a PITA, and is not easy (it doesn't bend that easily).

It really sounds like you need another circuit anyway.

Re: OT - Circuit Breaker question

#5

Re: OT - Circuit Breaker question

Tim Caley - North Little Rock

>Thanks to everyone that responded. I just love this place. There is always someone that knows the answer to questions here.

I have no intention of going anywhere near the inside of the breaker box, I was just trying to understand what would be needed.