Seeking electrical advice

Posts

Seeking electrical advice

#1

Seeking electrical advice

john pickett

>This sounds logical to me. However I have only done basic wiring.

My shop is in an underpowered garage in my rented home. I have a lathe, shop smith, grinder mini late, and hand power tools. So far I have been able to get by, but I really need a dedicated circuit for my shop smith.

There is a 220 dryer outlet in the utility room. Since I don�t have an electric dryer, it is not being used.

I was thinking that I could get a dryer plug & cable, wire each hot into a separate outlet and have two extra circuits to pull to the shop.

What do you think?

Re: Seeking electrical advice

#2

Re: Seeking electrical advice

Wayne

>each leg of the 220 is 110volts but you need to put two 110 brakers inplace of the 220 braker. Then you can split the 220 at the outlet where the dryer plugs into. Need to know what size the wires are running to the Dryer outlet.

Re: Seeking electrical advice

#3

Major “whoa!” here.

Rod Peterson -- Ormond Beach

>Give us an idea of the age of the house. Up until about 2000 it was permissible to run a dryer circuit with 10/2 (with ground) cable. Whatever internal electrics there were on the dryer that required 120V, were permitted to use the ground wire as the neutral (it's sometimes known as the mobile home exception). Since then, the dryer cord (and range cords) must be 10/3 (with ground), to permit a true neutral and a true ground.

You would be perfectly alright running your 240V saw/jointer/planer/dust collection/compressor on that 240V circuit, because none of them have any 120V electrics and don't need a neutral. But don't think of using the circuit to split into two 120V circuits unless it's truly a four wire cable.

Rod
Addy Protocol: Experienced amateur electrician

Re: Seeking electrical advice

#4

Also....

John in New Mexico

>I'd probably put some overcurrent protection on any individual 120v legs, sized to the wire you end up using. Just a little screw in fuse would do it.

John

Re: Seeking electrical advice

#5

Call a Pro !

SteveM

>You can't fool around like that with a rental. Or your own for that matter. Pay " The Man " and you'll sleep better.

Re: Seeking electrical advice

#6

Re: Seeking electrical advice

DB

>How far away is the utility room from the garage? The use of extension cords in place of permanent wiring is frowned upon by the NEC, fire marshall, tool manufacturer and probably the insurance company. Yes I know some of you have used extension cords without problems but that does not make it okay. The longer the extension cord the more problems you will have.

Re: Seeking electrical advice

#7

Re: Seeking electrical advice

JKJ in East TN

>If possible (and depending on the layout, breaker box capacity and other factors) I might run an entirely new circuit to the garage.

A forward-thinking landlord might even pay for part or all of the installation. Either way, if not extremely comfortable with house wiring I think most would highly recommended getting someone with experience to do the work.

JKJ

Re: Seeking electrical advice

#8

Might be missing something here...

Denis Ch�nard, Orl�ans, Ont.

>But the dryer plug has two 110V leads ("out of phase"), a neutral and a ground. At least that's the way I think these are wired around here...

Splitting this circuit into two separate 110V ones should be OK, provided that these new circuits are protected by some kind of fuse/breaker. I think the dryer circuit is 40 amps, so it should be ample to feed two 110V runs.

Am I missing something here?

DC

Re: Seeking electrical advice

#9

...but the world may come to an end

Rick Christopherson

>When I first read this question earlier tonight I didn�t respond because the answers were coming in with a balance of information. Now it seems that most answers are nea saying and a touch of fear mongering to boot.

As was said in the first couple of postings, if the dryer outlet does not have a 4-wire connection, then you cannot use it for anything besides a 240 volt load. If both the neutral and ground are present, then you can use this with a portable power distribution junction box for 120 volt loads. Because this is temporary power distribution you do have some options.

First and foremost, because your dryer outlet is likely a 30 amp circuit, then you must use #10 wire for your power cord. Without this, any overloading in your downstream circuits could cause an overheating in the cord. I am sure there are exceptions to this that permit smaller cord, and I�ve probably cited them in the past, but tonight I am not going to go digging through the NEC for references, so I am taking the conservative route.

Technically, you cannot put a 15 or 20 amp outlet onto a 30 amp circuit, so you would need to have some means of over-current protection at the junction box. In reality, I can tell you as known fact that most portable power distribution systems across the country have 15 and 20 amp outlets on 30 amp circuits. (Don�t misread this and assume this applies to permanent house wiring! I am speaking strictly of portable drop boxes.)

The only variation from NEC is putting a 15 or 20 amp outlet on a 30 amp circuit, and even this I cannot confirm as being in contravention in temporary wiring without doing some digging. The reason why I know that this is done across the country is because I build the test equipment that tests the portable distribution systems, and most of them are 30 amps.

To be completely within NEC guidelines, than all you would need to do is install 20-amp GFCI outlets in the drop box that have built-in 20-amp overcurrent protection (most do). So contrary to some of the postings, the world will not come to an end if you do this, and it can be done within the guidelines of the NEC.

Please note that if you were talking about a permanent installation, then my answer would be different, and I would not downplay putting outlets on 30 amp circuits...but that would be the only thing I would alter.

Re: Seeking electrical advice

#10

Re: Might be missing something here...

Dan Donaldson

>A lot of the older dryer circuits do not have neutral wires, just the two hots and the ground. That is the problem with trying to split them, no neutral.

Re: Seeking electrical advice

#11

Re: ...but the world may come to an end

Larry Clinton At Frankfort (Central)., Indiana

>Rick, I agree with most of your statements - but, #10 wire is not required for an extension cord. As long as this is not a permanent installation, the breakers are intended to protect the structure wiring, not the devices plugged into the outlets. Cases for my point, it is code to install 20 amp breakers - 15 amp duplex outlets (multiple) on the 20 amp circuit - and plug in an 18 gage extension cord to power a 100 watt table lamp (which is likely wired with an 18 gage cord). Many devices - Radios, TV's Stereos, Sweepers, lamps, etc. do not have wire size capable of tripping a 20 amp breaker without overheating and burning if the device gradually begins to draw the full 18 or 20 amps the breaker is capable of carrying without opening. The selection of the gage for the extension cord - provided the existing 220 circuit does contain a neutral and ground - should be based on the maximum draw of the equipment to be plugged into the circuit and the length of the cord.

Re: Seeking electrical advice

#12

Re: Seeking electrical advice

Barry Irby

>Are you proposing to put in a circuit that allows you to run a 220 machine (Shopsmith?) and then split the circuit into two 120 branches for outlets?

If so, the first part of the circuit should be protected by a 220 breaker. This is a tricky bit of wiring and probably should be done by a Pro, but do not put in two single breakers as someone suggested unless there is no 220 in the circuit.

Another thought: I imagine your Shopsmith will run fine on 20 amps @ 220. So you could run a four wire 220 circuit for it and then split that down to two 20 amp 120 volt outlet circuits. This might only require that you change the dryer breaker from whatever it is now (30 amps?) down to a 20 Amp breaker and save the thirty to put back in when you move out. If the dryer is wired on No 10 wire with four conductors, you could do that. (You can have the breaker SMALLER than the capacity, just not larger.) This would eliminate the controversy of have 20 amp outlets on a 30 amp circuit.

Re: Seeking electrical advice

#13

OK, got it

Denis Ch�nard, Orl�ans, Ont.

>I guess that makes me not as old as I thought :-D

DC

Re: Seeking electrical advice

#14

Re: Seeking electrical advice

john pickett

>Everything I,ve go (including the shop smith) is 110. I just wanted something on another circuit.

However, all of the fine advice here kind of makes me think that unplugging things everytime I want to use something else is not so bad after all. :)

Re: Seeking electrical advice

#15

Re: OK, got it

Kent in Emmaus, PA

>Candian codes required 4-wire dryer circuits earlier than the US NEC.

Re: Seeking electrical advice

#16

Re: ...but the world may come to an end

Rick Christopherson

>While your statements are correct for 15 and 20 amp circuits, I was not/am not sure they are applicable for 30 amp circuits. There is actually a good chance that they are not applicable for 30 amp. Unfortuantely, as I said last night, I just didn't feel like looking it up, so I wanted to take the safe route. I would rather be wrong at a safe answer, than to be wrong at an unsafe answer. (And I'm still too lazy to look it up.)

Re: Seeking electrical advice

#17

Re: Seeking electrical advice

JoeW in Detroit, MI

>John,

I haven't read all the responses to your question, but if nobody has already, I'd like to suggest that if you do run a cord from the outlet, think about using a GFCI at the outlet end. If you were to pull a new circuit into the garage, you would be required to protect it with a GFCI.