Re: Overheating 3/4HP motor
Rick Christopherson
>First off, a 3/4 hp motor won't be drawing enough current by itself to cause an appreciable voltage drop in the lines unless something is drastically wrong with the wiring. Your full load current draw will be less than 7 amps, and just for comparison, this is almost half of what a bathroom hair dryer draws. However, other loads in the area can cause a voltage drop. Cooling equipment that is on the same subsystem within your facility can have an effect on other parts of the system.
The cooling fan on the motor is designed to dissipate heat generated by the motor, but it is not designed to dissipate heat caused by other means, such as the sun. If this motor is exposed to direct sunlight, you can have a temperature rise that is easily an extra 20 degrees above ambient. Running over temperature can cause components within the motor to expand and the added friction can cause a loss of output power.
The same is true for the thermal overload protection. Even if the motor wasn�t exposed to direct sunlight, the thermal overloads could be, and this will result in their activation well below the normal current levels.
Another aspect is the duty cycle of the motor itself. If the duty cycle of this motor was related to temperature, and the motor was starting and stopping frequently, then the temperature of the motor will be higher than if the motor remained running continuously.
Because this is such a small motor, it is doubtful that rewiring it for 240 volts would correct the problem. If you have a line drop at 120 volts, you will probably still have a line drop at 240 volts too. That's because a line drop (if one exists) is probably not directly caused by this motor, but by another device.