#1

Unisaw plug and cord - flimsy?

Dan Manturi

>I recently wired my garage for 220V. I have a Grizzly 1029 dust collector (been in the corner since 1998, when I bought it new - no 220 in the garage) and they advise to put a Nema 6-20 twist lock on the cord. I bought a used Unisaw and, to my surprise, the plug on it is a 15 amp standard 220v plug. I understand that the Unisaw pulls about 14 amps, but the cord going from the switch to the motor actually looks heavier than the cord going from the switch to the plug. I was thinking of opening the switch box and putting some 12 gauge wire and a Nema 6-20 twist lock on there but figure Delta knew what they were doing. I have this on a 20 amp breaker, of course. The advantage of a twist lock is not a factor for me as I work alone and no one will tamper with the plug. Just wondering if anyone rewired this and, if so, is there any mess inside that switch box?

Thanks.

Re: Unisaw plug and cord - flimsy?

#2

No.

Rod Peterson -- Ormond Beach

>You had it right in saying “Delta knew what they were doing.” That NEMA plug they put on there, although it's a 15A plug will readily plug into either a 15 Amp or 20 Amp dual polarity receptacle. My DJ-20 jointer and my DC-380 planer use the same plug and cord assembly as well.

The one inconsistency I exercised in my shop was in the ceiling drop I installed, on which I installed a NEMA L6-20R locking receptacle, and used a L6-20P on the short converting wire (with a 6-15R on the other end). I wanted the short cord not to fall out of the ceiling drop, but didn't care at the point two or three feet above the floor.

I would be inclined to use the same plug on your DC (6-15P) so that you'll have compatible receptacles all around the shop. And if you use the dual polarity 6-20R receptacles (you must use 12 gauge wire and 20A breakers to use those, however), all of the tools will fit anywhere.

Rod

Re: Unisaw plug and cord - flimsy?

#3

Whats the actual wire gauge?

Kent in Emmaus, PA

>The wire gauge is printed or embossed on the cord jacket. I'm guessing its 14 ga. Assuming a 10 ft cord, the difference between 12 and 14 ga wire amounts to an underwhelming 0.02 Ohm. Really no reason to change it.

As for locking plugs, I see no cause for them on stationary equipment. If a plug gets pulled out becase of walking or tripping on the cord, re-route the cord in a safe location. If the plug falls out on its own, replace the receptacle. Locking should not be necessary.

Re: Unisaw plug and cord - flimsy?

#4

Re: Whats the actual wire gauge?

Dan Manturi

>Well, it appears to be 14 gauge from the plug to the switch, but thicker from the switch to the motor. I have not looked on the jacket. I bought some flexible #12 wire for running from junction boxes to tools using cords, and it is not as big as that, so I'll assume #14.

bottom line - these 2 responses seem a lot more informed than my knee jerk reaction, so I'll just leave it as it is and thanks for the info. Changing the dust collector to match the Unisaw seemes like a nice idea, but since I already sprang for the twist lock for that, I'll stay with it.

Best Regards,

Dan m.