>I want to make-up and install a exhuast fan for my basement. I would like to have it controlled by a humidistat. Looking at the Grainger website I see the humidistats but they are for 24 volts.

What do I need to make this work? The fan will be 110v.

Thanks!

Re: O.T. Electrcal Question

#2

Re: Sounds Like a Job For

Mark Mandell - Gone Round In Jersey

>TRANS-FORMERRRRRRS!

Well, actually the electrical step-down, 120 to 24v kind. McMaster-Carr and such will carry them. Think you'll also need a 24v contactor to turn on the line voltage fan.

There are, however humidistat-controlled fans sold as a unit, so you might save yourself a fair amount of trouble that way.

mm

Re: O.T. Electrcal Question

#3

Re: O.T. Electrcal Question

Tom MacGregor

>If humidity is the problem an exhaust fan may not be the way to go. If you run an exhaust fan you can't get your humidity level lower than that of your make-up air. Although line voltage humidity controllers are available that could run a fan, a $150 Sears dehumidifier did the trick for me and cost less than a controller, fan and set of louvers for the outside wall. It even cleared up the moisture left after I mopped up a 1/2" of spring flooding on a concrete floor last spring in about 3 days.

Re: O.T. Electrcal Question

#4

Re: O.T. Electrcal Question

Charles Williams

>First, what size fan? If less than 7.5 amps check out Grainger # 2E082 that does not need 24 volts. If more than 7.5 amps but less than 13.8 amps ( 3/4 hp ) look at Grainger # 2E852 that has a transformer and relay together to go with the humidstat that you saw. This would provide 24 volts to run to the humidstat and back to pick up the relay and operate the 120 volt fan.

Re: O.T. Electrcal Question

#5

Re: O.T. Electrcal Question

Kent in Emmaus, PA

>Grainger item 2E082 is a Honeywell wall-mount, 120V humidistat. We have one just like it in our 40 year old home, controlling a bath vent fan. For that application it works fairly well. But I have to agree with Tom McGregor that it probably wouldn't help much with basement dampness.

Re: O.T. Electrcal Question

#6

Re: O.T. Electrcal Question

Barry Irby

>Two or three things.

I thought many of the Borgs carried attic ventilation fans that had both temperature and humidity control/sensors attached to them. Check them out. You may be able to buy the sensor/controler alone.

My other questions revolve around where you live and what you are trying to do. If you are trying to reduce your humidity level by ventilating, then I don't beleive it would work where I am, in humid southside VA.

Ventilation, by definition is a flow through situation. Passing warm humid air through a cool space is unlikely to dry it out. If you bring in warm humid air and cool it down, it's relative humidity can go up dramatically.

There is a company advertising such a device and it has a fan that they claim is variable speed and runs all the time. When the sensor indicates, it runs faster, but it run constantly. They say the make up air comes back in from outdoors through cracks and leaks.

The problem I see is that no matter how that air gets in it brings its heat and humidity and polutants with it. This sort of system will make your AC run harder and has the potential to cause other problems like condensation inside walls etc.