Running 220 to Garage - 50 amps?

Posts

Running 220 to Garage - 50 amps?

#1

Running 220 to Garage - 50 amps?

Dan Manturi

>Hello all.

Finally running a 220 v line to my garage. Got rid of my old Contractors saw and got a 3 hp Unisaw, so I need to. I am not planning on a lot more 220V stuff out there, and certainly not a lot running concurrently, as I am alone when I work. I am planning that 50 amp, #6/3 copper is enough to run from my main panel (it is only a 60' run) into a load center. I wll have the Unisaw and a 2HP dust collector as the only things running at the same time, and maybe a couple of 20 amp 100V outlets, as I already have a couple of 100v 20 amp circuits out there. I really do not want to step up to #4 wire - the stuff ir really pricey - and I think that the #6 wire on a 50 amp breaker is enough, but there are greater minds than mine on this forum.

Looking for some feedback on this.

Thanks.

Dan M.

Re: Running 220 to Garage - 50 amps?

#2

Pocket ref sez...

John in New Mexico

>You can run 105' at 240V, 50A on 6 awg wire and still have less than 2% voltage drop. So unless someone trumps that with better info, I'd say you're ok with the wire.

As to outlets, that gets more complicated, and you might want to set it up as a sub-panel with circuit breakers for individual circuits.

Re: Running 220 to Garage - 50 amps?

#3

Re: Pocket ref sez...

Dan Manturi

>Yes, I plan on the unisaw on one breaker, the dust collector on another breaker, and then two 2 amp circuits in the panel.

Thanks!

Re: Running 220 to Garage - 50 amps?

#4

Re: Running 220 to Garage - 50 amps?

arw01

>If you have not priced the copper line wire yet, prepare for sticker shock!

For my shop, which was 75', I ended up with aluminum to run from the house panel to the shop panel. Less than $100 compared to $500 for copper. I was running 100 amps, so the difference will be less, but you are still talking quite a bit of dough.

Alan

Re: Running 220 to Garage - 50 amps?

#5

I'm not an electrician, but...

Ellis Walentine, Host

>...be careful with aluminum wire. Make sure you get the professional scoop on galvanic reactions and heat/shrinkage issues. After my fire, I learned enough to be extremely cautious.

Cheers,

Ellis

Re: Running 220 to Garage - 50 amps?

#6

Re: I'm not an electrician, but...

Dan Manturi

>Actually, i will settle for 50 amp with 6/3 copper rather than more and use aluminum. Reality is my stove was wired with this huge aluminium and as long as you use a large gauge, it is probably OK, but I am a copper guy when it comes to electricity.

I know and respect a lot of folks who use aluminum and appreciate the suggestion, but I am going to stay copper. It is a real shame but true that Aluminum is mush cheaper.

Dan M.

Re: Running 220 to Garage - 50 amps?

#7

Re: I'm not an electrician, but...

Howard Norman-Prescott, AZ

>I think that you are doing the right thing by using copper wire. Aluminum is certainly cheaper but there have been too many fires over the years for me to use aluminum.

Howard

Re: Running 220 to Garage - 50 amps?

#8

Re: I'm not an electrician, but...

Dan Manturi

>Did I say mush cheaper? I only had one beer. Much cheaper.

Dan

Re: Running 220 to Garage - 50 amps?

#9

JL

Re: I'm not an electrician, but...

JL

>If you get a breaker box that specifies aluminum or copper, aluminum should not be a problem for your main line. My main line in to my sub panel is wired with 4/3 aluminum.

Re: Running 220 to Garage - 50 amps?

#10

Re: Running 220 to Garage - 50 amps?

Kneale Brownson in Northern MI

>What's the difference in price per foot between the #6 and #4? My thoughts are that you already discovered you didn't have enough power. What happens if you get a couple more big tools? If it's going to cost you, say $225, to run #6 or $300 for #4, considering the work involved, I'd spend the extra few bucks.

Re: Running 220 to Garage - 50 amps?

#11

Re: Running 220 to Garage - 50 amps?

Bill Howatt

>I'd say you are fine if you are a 1 man operation. I run my shop off a 240V 40A panel and have never tripped the breaker. This includes lighting, a 2HP TS, a 2HP DC, and 2 shop-made air filters with furnace fan motors running together. There is also an old refrigerator and some house lighting running off it as well. You also mention a couple of other 20A, 120V circuits as well which is extra insurance.

Remember that your 50A at 240V is 100A at 120V.

As far as aluminum wire goes, I don't consider it a hazard IF it is installed properly with devices rated for aluminum and it must be installed properly. I had a house with both copper and aluminum and I had a problem with a loose neutral conductor in the main panel - it was a copper one!

Bill

Re: Running 220 to Garage - 50 amps?

#12

Re: Running 220 to Garage - 50 amps?

Dan Manturi

>Thanks all for the input. I'd say say at this point I am OK with the 50 amp and putting in a good sized box in the garage. If I am affluent enough or do enough work in the future to warrant another 220 v tool, then I guess I'll spend the bucks on a new piece of wire to the box.

Sound like the 50 amp is "enough" and I cannot think of adding another 220V tool I'd want to add in the future. Nobody in there but me.

Regards,

Dan M

Re: Running 220 to Garage - 50 amps?

#13

Re: Running 220 to Garage - 50 amps?

Marv

>Hi Dan,

Copper wiring causes fires too.

When aluminum is used by the professional electricians, they will coat the connections with some kind of glop that seals the connections from the atmosphere. Aluminum will oxidize and cause a problem if the connection isn't tight enough. Same goes for copper for that matter. I'm not an electrician but that's what one told me once. Before I wired my own house that I built, I called an electrician and ask him what his hourly rate was. This was a few years ago, he said $20.00 per hour. I then asked him if he'd come to my house and answer questions for an hour. Believe it or not he did. You can learn alot in an hour if you ask the right questions ....Marv

Re: Running 220 to Garage - 50 amps?

#14

Re: Running 220 to Garage - 50 amps?

Dan Manturi

>I have some electrician friends, and they all are pro copper and also advise on the wire and breaker size, but I like to get opinions from woodworkers who have been there and done that on breaker and wire sizes they use.

Thank.

Dan

Re: Running 220 to Garage - 50 amps?

#15

Re: Aluminum failure - causes - long

Larry Clinton At Frankfort (Central)., Indiana

>I kind of disagree, aluminum is used extensively by power companies for their drops from transformers to the meter base - but, I have had issues even with the aluminum drop outside my house. It became intermittent in one splice and I was losing half my house circuits (and all 220V). I did electrical work professionally for several years (over 30), so found the problem myself. It wasn't too hard as fire was flying out of the splice when I was tracing the problem. They replaced it, but I sure wouldn't have wanted it INSIDE my home. I have seen many failures of "properly" installed aluminum wiring. These include many mobile homes manufactured during the 1970 - 1980 era. I absolutely refused to work on any such home as I feared another problem wire would cause a fire and I would be blamed. I subcontracted all the HVAC and electrical work from a local Sears store for about 20 years (as a side job). During the Hunt brothers attempt to capture the copper market, prices of copper skyrocketed and Sears started to install Central air units using Aluminum (Corporate suggestion). I refused as I had seen too many failures in supposedly correct installations (Aluminum rated connectors, anti-oxidant coating applied, proper sized wire etc.). The store manager tried to convince me to use it, I told him to find someone else to install. He relented and I used copper. About 6 months later, corporate Sears issued a memo stating that no aluminum should be used and warranties would not be honored if any installed after that date. This was due to several lawsuits involving fires and - not sure - I believe at least one death. Needless to say the local manager was quite relieved and thanked me for my foresight and stubbornness. The major issues with aluminum are threefold. These are the expansion ratio, the softness, and the fact the oxides are not conductive. First the expansion rate is many times that of copper, therefore as the wire warms as it carries an electrical load it expands tremendously, as it expands - due to its softness, the connectors embed into the aluminum causing dents etc. When the load is taken off the aluminum contracts and the connector is now "looser". As this cycle continues the aluminum oxides in those areas where a gap occurs and more heat builds up - the aluminum becomes even more loose in the connector. This "loose connection" in conjunction with the non-conductive oxide causes high resistance in the joint. As this occurs, there is arcing and very high heating at the connector, eventually causing catastrophic failure. In most cases the circuit just opens up (if the connection is in a properly installed main etc.), but in a few, the excess heat and arcing will start a fire. In some ways I am frugal, but I can't see saving a few dollars and taking that chance. Many people store gasoline in unapproved containers in the shop or garage and get away with it, but I store mine in an outside shed. I do store flammable solvents in my shop, but they are in the original containers and in a metal storage cabinet with closed doors. I like to choose the chances I take, some things just aren't worth the risk.