>As long as I've got the terrace dug up I'd like to run an outdoor outlet to my shrubs for Christmas lights. Going under the sidewalk am I better off with galvinized steel of some PVC conduit ? No rush so can go either way. Just wondering wich would last " forever ".

Re: OT: Under sidewalk conduit . . .

#2

Re: OT: Under sidewalk conduit . . .

Ron Bauman

>There is a flexible cable made for under ground use. I'm not an electrician, but have used it and seen it used by our power company. Just make sure you bury it deep enough to avoid gravel and stones; there's probably a code that'll tell you how deep to go.

Re: OT: Under sidewalk conduit . . .

#3

Re: OT: Under sidewalk conduit . . .

Dan Donaldson

>Just use cheap black plastic pipe and direct burial wire.

Re: OT: Under sidewalk conduit . . .

#4

Re: OT: Under sidewalk conduit . . .

Bill Hammond, Oregon Coast

>If I remember correctly, Ridgid conduit with waterproof connections can go at any depth even on the surface, plastic and direct burial needs to be 2 feet down and in a bed of sand. Don't forget to put in on a GFCI protected circuit and not just with a GFIC outlet at the end. That outlet will get damp and give you false trips, ya don't want to be out in the snow Christmas eve relighting santa..

HTH Bill

creative spelling, the new art form

Re: OT: Under sidewalk conduit . . .

#5

Re: OT: Under sidewalk conduit . . chipmonks.

Kneale Brownson in Northern MI

>And hope the chipmonks don't decide to chew on it.

I'd opt for PVC and be sure to clean out the burrs where you cut the pipe.

Re: OT: Under sidewalk conduit . . .

#6

Grey Electrical PVC ONLY

Brian in Brighton

>You can't bury any other conduit but the grey electrical PVC. It is cheap and easy to deal with, size is identical to sch40 white pvc. You glue it up just like PVC. This is code on Colorado. You can put in std romex inside it.

I just put 450 feet of it in my yard for Xmas tree lights on 8 trees and 4 driveway lights.

You can put in direct burial wire, but it is far more expensive and to me not worth it. I used the cool 90 degree sweep elbows then went up to the electrical box with a GFI outlet so I also get a little support for the box to plug into. Don't forget the covers needs plastic clear over-covers now. You can find them at any Borg.

Brian in Brighton.

Re: OT: Under sidewalk conduit . . .

#7

Thanks Brian, I figured . . .

s.mackay@worldnet.att.net

>as much as I wanted it to be my origanal idea I knew better. As far as outlets wich way did you go ? I thought of hiding it in the shrub. The whole run will be " switched " from inside the garage at the " Christmas Light Control Station ".

Re: OT: Under sidewalk conduit . . .

#8

Re: OT: Under sidewalk conduit . . .

Larry Clinton At Frankfort (Central)., Indiana

>I'll second Dan's response. If it were me, I would use the flexible black (cheap) pipe in a large enough size that the wire could be replaced in the future if the need arises. I would then use UF wire. I would install the GFI outlet at the end of the line in a standard outdoor box. Reason being, capacitance of long buried line's can cause false tripping of GFI circuits. (Been there, done that).

Re: OT: Under sidewalk conduit . . .

#9

Re: OT: Under sidewalk conduit . . .

Sawdust Everywhere!

>I would use PVC for that work. I would use grey PVC which is more resistant to UV light than white PVC. I ran a lengh of about 90' of 1-1/4" grey pvc 24" deep from house to garage/shop with 4 x 6G wire for a subpanel in the shop.

Here in my city, code requires aboveground pvc to be schedule 80 (thicker wall than schedule 40), underground schedule 40 is enough.

If it's a short run, I'd just go with schedule 80 all the way! It'll last a long time. I'd sat at least 30 years.

Re: OT: Under sidewalk conduit . . .

#10

Is there an " outdoor " GFI . . .

s.mackay@worldnet.att.net

>or is it the " box " that makes the rig " outdoor " ?

Sure glad I asked about this ! Most of these suggestions never even entered my pretty little head ! WHEW !

Re: OT: Under sidewalk conduit . . .

#11

Its the box...

John in New Mexico

>Or rather, the box and box cover. You want a drip-proof cover and a raintight box. PVC is easiest to seal, but you don't need to put the whole thing in conduit, just bring the wire up through a foot or so of conduit below the surface, and attach the box to a stake or something a good foot or 18" off the ground. The other thing about GFCI's is that they don't like being on shared neutrals and can have false trips as a result.

John

Re: OT: Under sidewalk conduit . . .

#12

Re: Its the box...

Rob Stokes in North Vancouver

>I wanted GFI protected exterior outlets for my shop, so I dedicated a circuit, installed a GFI outlet on the interior of the shop and slaved the exterior outlets off it.

Worked great and allowed me to use conventional (read cheap) exterior outlet covers!

Rob

Re: OT: Under sidewalk conduit . . .

#13

Sounds like Rock-N-Roll ! Danke !

s.mackay@worldnet.att.net

>

Re: OT: Under sidewalk conduit . . .

#14

Re: Thanks Brian, I figured . . .

Brian in Brighton

>I put a duplex GFI in a single outdoor waterproof gang box. Then I used a watertight cover and we have to have a clear plastic one to cover that up too here in Colorado. The plastic cover forces you to have the wire run downward thru the notches in the bottom of the cover. This way any rain will not run down into the outlet. I have not tried it full scale, but the outlets seem to work. I placed mine facing the tree so that the lights wire will plug right into it with little drap. They are about 6-8 inches off the ground, so snow might not be a problem. Although last winter was an off one for us.

Good luck.

Brian in Brighton.

Re: OT: Under sidewalk conduit . . .

#15

Polypipe is a no-no.

Brian in Brighton

>I think the NEC does not allow polypipe to carry electrical wire inside it. Besides, at $1.35 for a 10 foot piece of grey PVC how cheap do you have to be to not use something that meets code?

You might be able to run 'direct burial' wire inside of the polypipe and meet code, but I doubt it and the cost of the wire alone will drive you away. Here in town it's about $1.50 per foot for 12/3. While I got a 250' roll of 12/3 romex for about $50, 250 of PVC is around $35, some fittings for both ends you will need irregardless of the wire so the cost is the same. Seems like a no brainer to me. I'm just the guy for that :-0

You have to remember that the codes are designed for a reason. I had the moron who remodeled the basement in my old house not care about codes and to say he did a rotten job is giving him credit. For this wiring, I can see someone digging along one day in the future. Finding the polypipe, mistaking it for old irrigation, and wanting to remove it. Then the guy will take his shovel to remove it and BLAM!!!

Same goes for pvc. It's white for potable water, purple for non-potable water. You can put it into the ground on your own in any fashion you want, but you should not mix water types in the same color pipe on the same property. We used white pvc for all our outside water, all of it is non-potable so there is no mixing of water types in the same property. Businesses MUST use purple for non-potable in Colorado, it's the law.

Same for gas pipe. Black pipe is required, if you use galvanized you will be replacing it when the inspector comes around as the gas will corrode the zinc at the joints and you will get a leak. Zinc can be used for air lines and such, but not natural gas.

Brian in Brighton.

Re: OT: Under sidewalk conduit . . .

#16

Re: Polypipe is a no-no. I don't believe what I

Larry Clinton At Frankfort (Central)., Indiana

>recommended is against code. If you run UF wire (sheathed direct bury / sunlight resistant wire) as I recommended - you do not even need to use conduit or pipe or anything else. I do not believe - don't have a code book any more - there is any stipulation against running the UF wire in or through ANY kind of pipe. By the way - for your enlightenment - many codes were written at the (lot of money spent) request of interested groups. For instance - in Cook county Illinois, metal chimneys were banned - all chimneys had to be masonry. Guess who decided these were "safer" - the union. In the 50's metal conduit was required for new residential wiring in areas of either Florida or California - can't remember which - Again at the lobbying of the union electricians / contractors. This requirement was canceled after a few years - and a few deaths caused by electrocution. Seemed the salt air corroded the conduit fittings and connections to the boxes. This in turn caused loss of the ground as the conduit was used for that purpose. This wasn't the worst,as the corrosion, in some cases shorted out the line to the conduit at the main, causing all the "grounded" areas of the line to be hot. This included kitchen appliances - the outside case's of the toaster, mixer etc. I believe they have banned the use of conduit in those areas now. Good common sense is really needed when wiring, plumbing as much as a code book. I have seen arguments among several experts when applying some of the requirements of the NEC codes. There are websites dedicated to interpreting the codes.

Re: OT: Under sidewalk conduit . . .

#17

Re: Grey Electrical PVC ONLY

Bruce Wrenn

>Box has to be physically supported by something other than conduit- NEC requirement. By using PVC, you can change out condutors in case of failure, or upgrade. I never bury UF cable any more- costs the same to trench, but if you ever have to changei it, you have to retrench. Don't use 1/2" either as it will only hold one set of wires.

Re: OT: Under sidewalk conduit . . .

#18

Run a few extra conduits

Mark Goodall - ATL - tooljunkie

>When I had my walkway up and was digging, I decided to lay several extra pipes underneath for future use. So when the time comes to put lawn sprinkler system, or have any other reason to put something under the walkway, I just have to dig down about 10 inches right beside the concrete and I'll find 2 or 3 pipes of various diameters.

Happy Woodworking!

Re: OT: Under sidewalk conduit . . .

#19

Re: Polypipe is a no-no. I don't believe what I

Brian in Brighton

>Larry, Apologies, I did not understand that you wanted to bury direct bury wire inside the polypipe. What would be the purpose of this? Just shovel deflection prior to cutting? Would it allow you to bury it in less dirt?

Could not agree more on the stupid codes that are out there. My experience is that people will do anything to save a buck and that includes burying Romex, using co-ex non-pressure PVC for water lines, no regulators on the water lines, making 5 in-line connections along a wire run to keep from having to buy more romex, etc. My old house had many junction boxes in the attic and basement that had wires going in and out with no logic. Of course this moron tied some wires to the wrong side of the CB so that you could not shut off some lines in the house. He had multiple terminations on a single CB. Best of all was the 4-plex box with the extra holes drilled in it so he could have 9 romex lines going into it!! They only come with 8 holes, so let's drill another to make it work.

SWMBO bought the house before I came along. So I got to deal with it.

I still stand that it is a bad idea to run the wire inside water lines. Maybe he can wrap caution tape around the line so that anyone in the future will realize it is not an old water line that is not being used so he can cut it out and get electrocuted.

Brian in Brighton

Yes, the boxes are supported by a 2x4 PT board. It is stiffer and makes it easier to plug into. I did not know this was code.

Re: OT: Under sidewalk conduit . . .

#20

Re: Polypipe is a no-no. I don't believe what I

Larry Clinton At Frankfort (Central)., Indiana

>Brian, the reasons to use the pipe are #1. It is much easier to force a pipe under a sidewalk after doing trenching to each side. In many cases you can hook up a hose to the pipe and "drill" under the walk with the water. #2 If at some time in the future the wire requires replacement due to damage, wanting larger wire gage, etc. It is very easy to replace the wire without re-trenching. I suppose the pipe does add additional protection, but all my electrical conduits that are buried have yellow plastic tape a few inches above the pipe to alert anyone digging or trenching.

Re: OT: Under sidewalk conduit . . .

#21

Re: Polypipe is a no-no. I don't believe what I

Brian in Brighton

>Larry, We must think alike. I also put down yellow caution tape in the trenches as I started to bury them to warn people. Mostly SWMBO needs this. She is a gardening fool and would think nothing of chopping into the dirt a little harder since we have a clay based soil here.

I would still avoid polypipe and go with grey PVC, stiffer and stronger.

Brian in Brighton.