David W

>We will be having a concrete floor poured soon in our new barn/shop. I'd like to have power run to some 220 and 110 outlets to several spots within the shop space that will not be adjacent to a wall. We will have an electrician actually do the wiring and lighting once the space is roughed in. They have already placed the panel and put lights up in the barn space. We could have hanging outlets for the interior locations, but I think I prefer pedestal type outlets that would be serviced from underfloor wiring. I could run the conduit and wiring myself before the slab is poured. Any specific suggestions on this? I will have three 220 outlets each on a separate circuit to power a 10" cabinet saw, 8" jointer and 15" planer. My wife would like a couple of 110 outlets in her area for her sewing machine, serger or quilting machine. Is this something I should do or just grit my teeth and have the electrician out now. My father was an electrician and I pulled a lot of wire with him over the years. The idea of me having someone else do this would not have set well with him.

Re: new shop wiring

#2

Re: new shop wiring

Thomas Skaggs, Foothills of Mount Level

>My suggestion is to plan for more outlets that you currently think you'll need. You may have a layout for the tools you currently have but I find that workshops are evolutionary in nature. Over time you get more tools or re-arrange tools etc. If you don't have outlets everywhere then you limit the flexibility of your shop.

I also suggest outlets both low and high. Make sure you have plenty of outlets above workbench height. They become very key for handheld power tools etc.

Tom

Re: new shop wiring

#3

Re: new shop wiring *LINK*

David Harker

>I put 110v, 20amp outlets every 32" (every other stud) about 4.5 feet up.

Each outlet is on a different circuit than the ones on either side of it (2 circuits, the outlets alternate between them) - this was done so that when I plug something in to one outlet, and want to plug something else into a different circuit, I can just plug the second tool into one of the outlets to the left or right of the 1st tool's outlet.

I did the wiring myself (13 circuits, with lights, furnace, etc), so cost was limited to material cost. My electrician supervised, inspected, and did final hookup in the breaker box. A flexible electrician is a good thing! Also have several 220v circuits, some dedicated (dust coll, compressor), and some general purpose w/ multiple outlets (I work alone, only one major tool is on at once).

Put in way more than you think you will need.

Good luck!


Pics of my wiring progress

Re: new shop wiring

#4

Re: new shop wiring

Grant Smith

>I would suggest you buy some of the grey plastic PVC pipe 3/4" in diameter and install that yourself so it sticks up from the floor and can later be wired by your electrician.

Homecenters stock the pipe and even nicely sweeping elbows to make pulling in the wiring easy.

Just run from the wall beneath your electrical panel down under the surface of the concrete and then back up wherever you'll want power. It should be easy enough for your electrician to finish this once the concrete is set up.

The stuff goes together just like PVC pipe and will be easy to pull in wiring or even change it out as needed over the years. Just don't make more than 360 total degrees of bends or it will be difficult to pull in wire.

FWIW,

Grant in Iowa

Re: new shop wiring

#5

Re: new shop wiring/Fly me to the moon

Barry Irby

>I aggree with Grant. Run some conduit now. Easy to do and not that much money. You will appreciate it later.

I would also plan out where my major machines would be and consider running pipe in the floor for duct collection. My Table saw is fairly near a wall and I still hate stepping over that pipe. In my next shop.....

Re: new shop wiring

#6

Re: new shop wiring

C.W.Stivison

>As a fore thought I would run some cheap 1/4" rope in the conduit as I put it togeather so it would be real easy to pull in the wires.

CW

Re: new shop wiring

#7

Re: new shop wiring

Rick Christopherson

>Rather than having your PVC piping protrude from the floor, I would terminate each line in a covered vault below the floor that can be covered with a protective plate. There will be code issues to deal with for these vaults, but if you do your research now you can accomodate these requirements when it actually comes time to pull the conductor.

Re: new shop wiring

#8

Another alternative

Pat Evans

>I agree that pipe protruding from the floor is not optimum. What I used to do is stub the pipe up with a screw coupling on the end which is flush with the floor. While the concrete is being poured, install a piece of pipe about 2' long into the coupling as a guide to keep the pipe vertical. In the future, you can screw a short nipple into the coupling and install a box on that, or you can install a plug in the coupling if it is a spare or abandoned pipe. That way your floor will be flush regardless of where your conduits are. That method also allows you to install unobtrusive spare conduits.