Electrical Information CORRECTION
Mark Mandell - Gone Round In Jersey
>I'm posting this to bring it to the top of the Board because only a few people have seen the follow up message I put in the original thread started by Sawdust about allowed wiring.
"Well, Mr. Everywhere, I spoke to my local Code Dude and an electrician who I trust, and here's what I got back:
A. The 4-wire cable is, as before, absolutely REQUIRED for your double 110 setup.
B. You can switch the 220 circuit cable "upstream" with a Single-Throw-Double-Pole switch as long as it is disconnecting both hot leads of a single circuit and the switch is rated for the same or greater amperage as the circuit breaker.
C. You can have 2 circuits wired to separate halves of the same receptacle PROVIDED that both hot leads are controlled by a single breaker IN THE SERVICE PANEL, i.e. 2 breakers that are "bridged" like a 220 breaker, and the conductor tabs on the duplex ARE REMOVED to separate the 2 sockets from one another.
D. If the duplex receptacle being used is the only one on the circuit, it's rating must match the total amp load of the circuit breaker. So, if the 220 circuit's breaker is a 20 amp, then the duplex receptacal at the end of the line MUST be rated for 20 amps.
E. Even if you have a 4-wire cable, you shall NOT split it into two discrete circuits with independent breakers on each branch. The breakers MUST be linked/bridged. To use two independent breakers, the present cable must be removed from the service panel and replaced with 2 separately sheathed cables.
I think that corrects all the incorrect information I posted earlier."
I'll go back to my corner now. . . .
MM