OT Electric problems with contactor

Posts

OT Electric problems with contactor

#1

OT Electric problems with contactor

Ken Krawford

>Below is a picture of a contactor connected to my 5 hp dust collector. The line side is on the left of the photo, the load on the right and the 110V remote control terminals in the center. I was surprised (and alarmed) to see the discoloration/semi-melting of the connectors on the black line and white load terminals. The circuit is 20 amps 240 volts with about a 30 ft run of 10 gauge wire. Nothing else is on the circuit.

Any ideas on what the problem may be?

Thanks.


img

Re: OT Electric problems with contactor

#2

Re: OT Electric problems with contactor

John D. Luke

>Looks like the lugs were not crimped tight enough, causing a high resistance connection there.

Cut back to clean wire and crimp on another lug making sure that it is crimped properly.

I use crimpers that rachet down and won't release until they are fully crimped. Around here they are available sometimes at Boeing Surplus. I used to work for United Air Lines but won't say where mine came from.

Re: OT Electric problems with contactor

#3

Re: OT Electric problems with contactor

Bill Howatt

>I agree with John, it is a poor connection which results in a bit of resistance between the wire and the connector. If the resistance was only 0.01 of an ohm 20A flowing through it would result in 4W of heat to be generated in a very small area. The heating damage usually causes even higher resistance to the extent that the wire or something else will ultimately burn off.

Remove the bad connections and clean/replace where ever there is discoloring. Crimp connections are good with care and the proper tool but for high current use I always solder for good measure. I recommend you do this. You might as well do all 4 while you are at it. If you don't repair it you could seriously damage the relay connection area and have to replace it.

Bill

Re: OT Electric problems with contactor

#4

Re: OT Electric problems with contactor

Larry Clinton At Frankfort (Central)., Indiana

>The above posters are correct in that the "lug" was not properly crimped (or the inside of the lug or wire) had contamination when it was assembled). However, I disagree on replacing the "lug" and properly crimping or soldering it on. If you do put a crimped connector on the line they are correct. I would not replace the connector. This is an aid to assembly at the factory, they usually purchase or build wiring harnesses and it speeds assembly. I would cut the wire off past the discoloration, scrape it CLEAN, remove and clean the screws and hold down tab of the contactor (use a wire brush for this) and put the wire end directly under the tab. There is a corrosion resistant lubricant available at electrical supply houses that you could use to coat the parts - but I wouldn't deem it necessary for this fairly light load. Tighten the screws securely and you should have no farther problem. As an Engineer responsible for wiring of several complex automated assembly machines in my career, I have found the "connectors" to be a major problem in high amperage circuits. I even had one fail in my own furnace connected to the fan control relay.

Re: OT Electric problems with contactor

#5

Re: OT Electric problems with contactor

Bill Turpin in WNC mountains

>I agree, use the screw terminals. The spade terminals in the picture depend upon the spring tension of the crimp terminal for good contact. Any problem will cause heat which anneals the connector which reduces the spring tension. It becomes a self professing prophecy: it only gets worse. Most of the yellow connectors(which hold 10/12 wire) are not rated for twenty amps. Crimp connectors do not work with solid wire, picture is not good enough to tell which you have. Cut wire back to the point that the insulation will slip off. If it is tight, it has been partially melted.

Bill

Re: OT Electric problems with contactor

#6

Re: OT Electric problems with contactor

Bill Howatt

>I agree with that as well. My first look at the picture made me think the connectors were the ring ones under the screws but a closer look indicates they are the push-on types. Once the mating parts have been overheated it isn't a good idea to rely on them again.

Bill

Re: OT Electric problems with contactor

#7

Re: OT Electric problems with contactor

Matt Prusik

>I have a slightly different take.

If this setup were mine and I saw what you're showing inthe picture, I would be inclined to replace all of the wire in and out of the contacter assembly with 10 gauge material.

Also, if I understand you correctly, seeing these connecters fry on the line side of the circuit tells me there might be somethong wrong with the motor on the DC. The advice you have gotten so far is excellent. But I would not ignore the motor if there are indications of a problem with the load side of the circuit.

I would check the motor and be sure that it's spinning freely with no physical obstrucions (dust and chips binding the squirrel cage) Also I would check to see that the bearings are good by trying to move the shaft of the motor back and forth.

I know that this situation can be frightening. But even if you have to do some disassembly to check out the motor, it's a good investment of time and labor to head off a potentially expensive problem inamsuch as it can be a big expense to replace a single phase, 5 HP, 220 volt motor!

Good luck and best wishes!

Matt Prusik

Re: OT Electric problems with contactor

#8

Thanks for all the good advice

Ken Krawford

>I'm relieved that the consensus agrees it's the connectors. I've taken all of them off (yes they were spade type connectors) and wired everything directly to the screw post. Matt, the wire is 10 gauge and the melted terminals were on both the load and line side of the contactor. I'll check the motor to be sure it is rotating freely.

Thanks again for the help.