Wiring needed for 3hp/220v motor?

Posts

Wiring needed for 3hp/220v motor?

#1

Wiring needed for 3hp/220v motor?

Joe Pack

>I need to run a 220v line to run a single phase 3hp motor on a new table saw that is labeled as a 15 amp draw. The run from my sub-panel to the outlet will be about 25 feet. The instructions suggest a direct wired setup, but this is not practical for me, so I plan to install a cord of about 15' (10' would do, but the slack allows for adjustment if I need to). That would make the total run about 40 feet, maximum.

My limited experience tells me that a #12 3-wire cable and a 20 amp breaker will carry the load safely, and that a high quality #12 cord w/twistlock ends that I build myself will work just fine. Am I correct in this?

I already have a 220v 20 amp #12 wired circuit on one wall with 4 outlets for flexibility, but I only use one at a time to provide power to my dust collector (labeled 13 amps).

It is no harder to run a larger cable and build a heavier cord, but is it necessary? If I run a 30 amp circuit using #10 wire, I could add one or more extra outlets, but I seriously doubt I would ever use them, but....

What are your thoughts? Am I okay here?

Re: Wiring needed for 3hp/220v motor?

#2

Jesper, Denmark

Re: Wiring needed for 3hp/220v motor?

Jesper, Denmark

>There is never anything wrong with running an oversize wire. The incremental cost is miniscule and you neve know when it might be useful.

Re: Wiring needed for 3hp/220v motor?

#3

Re: Wiring needed for 3hp/220v motor?

Rob Sandow

>I think you are fine. For the cable running from the machine to the receptacle, I like to use the rubber jacketed cable because it's flexible. I usually go up one size on the rubber jacketed cable because it's stranded and easier to work with, but not on the romex from the panel to the receptacle (12ga is much easier to work with than 10ga). You can get this from the orange or blue Borg.

Re: Wiring needed for 3hp/220v motor?

#4

Re: Wiring needed for 3hp/220v motor?

Robert Egbert

>You are fine with 12/3 and L620 turnlocks. Don't go with 10/3 the wire may not be more but your plugs are almost double or more and you dont and will not need it. If you need to go bigger run a new ckt.

Re: Wiring needed for 3hp/220v motor?

#5

What I Did

Mike Fitterling

>My outlets are mostly 20 amp, but when I wired the shop I ran all 10 gauge wire to the outlets. I still put 20 amp outlets and 20 amp breakers in, just used heavier wire. Now, it was much harder to run, but if my needs change I can simply swap out the outlet and breaker for 30 amp with no deleterious effects. This has happened to me when I added a large compressor; I simply put in a 30 amp outlet and breaker in the box and was set. If you use 10 gauge you can still use the cheaper 20 amp plugs and outlets, but the heavier wire will give you options down the road. You also need to choose boxes wisely so they will accomodate the larger wire and any connections you have to make inside them.

As for an extension cord, 12 gauge will be fine for that short of a run for that motor. If the run was over 50 feet you would be wise to go up one size.

There are advantages and disadvantages to the twist lock connectors. Overhead outlets will definitely benefit from them but wall mounted ones may not. Mine are all straight plugs, except overhead. If you trip over the extension with twist locks, chances are you will fall, if you do the same with straight plugs, the chances are the extension will unplug instead. You choose.

Re: Wiring needed for 3hp/220v motor?

#6

Re: There are lots of options...

Jamie Donaldson

>.. when using #10 cords at your local RV supply store. We use #10 stranded runs every day, and in several convenient lengths.

Re: Wiring needed for 3hp/220v motor?

#7

Re: Wiring needed for 3hp/220v motor?

David sparks

>You are correct regarding the 12/3 wire. I used 12/3 when I wired the outlets for my 3 hp table saw and 3 hp planer. Everything works fine. I considered using 10/3 wire but decided against it after talking to a couple of electricians and consulting the people here on Woodcentral. If I ever need to wire up something that requires a 30 amp breaker, I'll install a new run of conduit for that machine.

Re: Wiring needed for 3hp/220v motor?

#8

Would YOU trust electrical advice from this guy??

Mark Goodall - ATL - tooljunkie

>With a name like Sparks I'm not sure if I'd trust electrical advice from you!

David, you know I'm kidding! (I hope)

I actually love the name. There's an electrician near here called "Mr.Sparky". I see his van from time to time.

Happy Woodworking!

Re: Wiring needed for 3hp/220v motor?

#9

Re: Would YOU trust electrical advice from this gu

Rob Stokes in North Vancouver

>I worked with two really good elec. designers - their names were Surge and Bang (truth!)

Rob

Re: Wiring needed for 3hp/220v motor?

#10

Thanks for the help.

Joe Pack

>