OT Wiring Question
Spence in RI
>Is it against code to have a 20 amp circuit breaker on 14ga wire? The circuit is in the shop only.
Thanks,
Spence
Knowledge You Can Build On — Est. 1998
OT Wiring Question
Spence in RI
>Is it against code to have a 20 amp circuit breaker on 14ga wire? The circuit is in the shop only.
Thanks,
Spence
yes
Joe Piotrowski - Chicago Burb's
>basically a wire can be bigger than sized for. never small. 20a = #12
location of the circuit has no bearing on the decision. ask your local village inspector, a qualified electrician or google over current protection.
Re: OT Wiring Question
Spence in RI
>OOPPPPSSSS!!!!! I'll snap a 15 amp breaker in there today. Thanks for the lesson!
Spence
Re: OT Wiring Question
Matt Berry
>The main reason that it is important not to size the breaker larger then what the wire is rated for is HEAT. If you start pulling close to 20a through 14awg wire, it will start to heat up (it's even better with the cheap 16awg orange extension cords everyone insists on using) Too much heat and your shop can burn to the ground. Electrical safety is very important.
Yes it is against code..Get to thinking that
Mike in Paradise
>now that we have breaker in houses no-one changes them to 20 amps which is good.
I remember in the houses with fuse panels where all the time you would find that someone had put a 20 amp fuse on a 15 amp circuit.
Breakers are a good thing!!!
Re: OT Wiring Question
Jim Swank
>The circuit breaker is sized to protect the wiring, not what's plugged into it.
new style fuses too...
John in NM
>that have different diameter bases so you can't up-size a fuse. Also too small to put a penny under the fuse - now I wonder if a dime would fit? :)
John
Re: yes - Ditto that
Ray Carson - Lawrenceville, NJ
>
Thanks Folks!
Spence in RI
>Changed it over this morning.
Spence