Electrical question

Posts

Electrical question

#1

Electrical question

Steve Schoene

>I need to run an extension cord in order to use a compressor OR my table saw for limited service in temporary quarters (a detached garage) with no 240 power (only 120). There is a 30 amp dryer circuit outlet in the house that I could use. The one way distance is 75 feet. The 240 amp draws are 14 or 15.5 respectively. These motors have been run on 20 amp circuits and currently have the appropriate plugs for that.

Is it correct that I would definitely need to terminate the extension cord with a 30 amp. female, and replug my motors with the matching 30 amp plugs?

Voltage drop calculators suggest that voltage drop would be less than 3% with 12 gauge copper wire. Is using that acceptable, or does the extension cord wire need to be 10 gauge and dramatically more expensive to match everything to the 30 amp breaker? (The wires will run through no walls and are strictly temporary use extension cores.)

Re: Electrical question

#2

Re: Electrical question

Sawdust Maker

>I would use a 10 gauge extention wire because it will handle more current. Furthermore, the extension wire will be rather long (75' or more) and it woul be better for both motor to run on a 10G wire.

As for termination, you can terminate the male end of the extension with 30A plug, and the female end keep it at 20A. Afterall, you're not drawing more than 20A from each tool.

Re: Electrical question

#3

Re: Electrical question

John in New Mexico

>I get about 1.8% drop for 75 feet (actually 150' in the calculation) on 12 awg. I'd definitely use the 12, as at 75' even 10 awg isn't quite heavy enough for a 20 amp chord (about 57', but thats at 2%).

Use whatever plugs you want- its for your own use, no?

John

Re: Electrical question

#4

Wire Gauges Switched?

Marvin Horn

>

Re: Electrical question

#5

Nope, wrong table (120V)...

John in New Mexico

>Nice catch.

Calculation for the 12awg is the same though, 1.8%. So you could use the cord for 30 A if it were 10 awg, comes out to 2.2% at 240 V (75').

John

Re: Electrical question

#6

Re: Electrical question

Bill Hammond, Oregon Coast

>Breaker and wire should match, you don't want a slow short to melt the wire or start a fire and not have the breaker trip. That said, being cheap I would use two runs of 12/2 romex and double them up in the connectors. After I am done with the temp setup I can use the 12/2 elcewhere where I may not have a use for the 10/2. As said earlier I would use a 30 on the plug end and a 20A rec in a handy box on the other end. Might even want to end it with a small breaker box with a 20A breaker and then mount a duplex 20A rec on the box.

All this is likely dangerous and stupid but if you are careful about not stepping on the wire it should work

Remember there being no common you can't split it and get 110

Re: Electrical question

#7

Re: Electrical question

Larry Clinton At Frankfort (Central)., Indiana

>Personally, I would run a 12 gage extension wire & use existing plugs on the saw. The breaker is meant to protect the wiring in the walls (permanent wirings only). If breakers were sized to protect extension cords, there would be no 18 gage lamp cords sold. Take a look at some of the plug in printer / shaver and other cords with the transformer a foot or so up the cord. I have some that must be 22 gage. I wired my shop using 10 and 12 gage wire (10 gage for the 220 - 3 & 5 hp large motors) and have 20 amp breakers. I have some tools - like the Dremel, that if shorted would have the cord become very hot or burn. This is a normal practice, in reality most of the time a short pulls much more current than the breaker will hold - causing a rapid trip without any wire heating. The most risk is using an undersized extension cord that cannot carry the load of the device being operated without excessive voltage drop and resulting overheating of the cord.

Re: Electrical question

#8

Re: Electrical question

Steve Schoene

>Thanks guys.